syarn
Silver Member
newark DE 2500 sf fast food salad restaurant. 2009 IMC.
existing restaurant being renovated to a new restaurant.
the design shows one existing air handling unit supply air 4000 cfm.
the existing return main duct 2650 cfm.
the engineer claims there was no outside air duct connected to the existing system....
the engineer adds a new outside air duct connected to existing return duct side of main system at 1350 cfm to satisfy make-up air for new exhaust fans aka the make-up air is coming from the main system (not separate).
the kitchen adds a new oven exhaust hood 880 cfm.
the serving area adds a new toaster exhaust hood 450 cfm.
the 2 bathrooms add new exhaust fans 75 cfm each.
the air balance schedule shows a (-130) cfm [1350-880-450-75-75].
is a separate make-up fan unit 1330 cfm required?
if the existing system DOES have an existing outside air duct connected would that condition than trigger need for an additional make-up fan unit?
existing restaurant being renovated to a new restaurant.
the design shows one existing air handling unit supply air 4000 cfm.
the existing return main duct 2650 cfm.
the engineer claims there was no outside air duct connected to the existing system....
the engineer adds a new outside air duct connected to existing return duct side of main system at 1350 cfm to satisfy make-up air for new exhaust fans aka the make-up air is coming from the main system (not separate).
the kitchen adds a new oven exhaust hood 880 cfm.
the serving area adds a new toaster exhaust hood 450 cfm.
the 2 bathrooms add new exhaust fans 75 cfm each.
the air balance schedule shows a (-130) cfm [1350-880-450-75-75].
is a separate make-up fan unit 1330 cfm required?
if the existing system DOES have an existing outside air duct connected would that condition than trigger need for an additional make-up fan unit?