• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

separation between B and S2

VLADIMIR LEVIN

Registered User
Joined
Jun 11, 2019
Messages
113
Location
NY
What's the separation required between B and S2?
From Table 508.4 looks like 2hours for NS.
But no separation is required between B and S1? But S1 is low hazard and S2 is moderate hazard.
Am I missing something?
 
It is based on fire load. Group B and Group S-1 have higher fire loads than Group S-2, so the separation required between the Group B and Group S-2 occupancies is to protect the Group S-2 lower fire load area from the Group B higher fire load area.
 
It is based on fire load. Group B and Group S-1 have higher fire loads than Group S-2, so the separation required between the Group B and Group S-2 occupancies is to protect the Group S-2 lower fire load area from the Group B higher fire load area.
What is a "fire load"? is it somehwere in the code?

p.s. I had it backwards- S1 is moderate and S2 is Low
 
"Fire load" is not defined by the IBC, but it is defined in NFPA's Fire Protection Handbook as the "measure of the maximum heat that would be released if all the combustibles in a given fire area burned."

Group B and Group S-1 occupancies have a lot of combustibles, so it has a moderate fire load, whereas Group S-2 occupancies do not include a lot of combustibles, so they have a low fire load.
 