Permit issued to install a 90+ furnace, installers took the two intake/exhaust PVC piping through the garage speration wall and out the gararge exterior wall below the 5/8" type-X drywall on the garage ceiling. Seperation wall between the furnace/rec-room side and the garage IMO has been breeched. I requested the pipes be covered with a minimum of 1/2" drywall to the breeched area . HVAC man claims he only needs to fire caulk around the PVC pipes at the seperation wall and I disagree. In a fire the PVC pipe would melt leaving a large hole in the seperation wall.
What do you think? Am I correct?