Service (Furnace) room separation from the remainder of a house with secondary suite- Not Required?

sunyaer

REGISTERED
Joined
Apr 21, 2022
Messages
338
Location
Toronto
Based on the following codes NBCC 2015 and OBC 2012, service (furnace) room of a house with secondary suite is not required to have fire rated separation between the service room and the remainder of the house, while NBCC 2015 requires continuous smoke-tight barrier to separate the service room from the remainder of the house, but in OBC 2012, this smoke -tight barrier is not required.

Is this interpretation correct?

This is from NBCC 2015 Division B:
1687900501014.png
_________________________________________________________________________________________________________________________
This is from OBC Division B:

1687901039173.png
1687900686042.png
 

Attachments

  • 1687901008448.png
    1687901008448.png
    6.7 KB · Views: 0
Appears to be an oversight in the Ontario code. I would say that the service room is usually considered part of one of the suites, and in that instance, it would be required anyway. However, if it is in the common area between suites, it wouldn't require anything.
 