Service Panel not quite ready?

jar546

CBO
Joined
Oct 16, 2009
Messages
13,000
Location
Not where I really want to be
This is a service panel for a single family residence. The 2" conduit leaves this combo enclosure to feed a sub-panel inside the residence.

How many violations do you see in this photo? Solely based on what you see.

IMG_2767.jpg
 
I can see the intersystem bond cover and the ground rod clamp laying in the bottom of the panel, and I can hear the electrician saying "You weren't supposed to be here 'til this afternoon."
 
Why is the green wire not the GEC?...Got it...missed that they were feeders....But then the GEC could be upstream somewhere that we can't see ...Like at the drip loop.....no?

E3607.2 Location of grounding electrode conductor connection.
The grounding electrode conductor shall be connected
to the grounded service conductor at any accessible
point from the load end of the overhead service conductors,
service drop,
underground service conductors, or service lateral
to and including the terminal or bus to which the
grounded service conductor is connected at the service disconnecting
means. A grounding connection shall not be made
to any grounded circuit conductor on the load side of the service
disconnecting means, except as provided in Section
E3607.3.2. [250.24(A)(1) and (A)(5)]
 
This cabinet appears to be intended for a bottom feed....but it’s not. Are the feed through lugs original equipment?
 
Last edited:
No, no it can't. We are talking at the point of the service connection either in the meter base or service disconnect.

Jeff...Are we talking about the same thing? 250.24(A)1 allows the GEC to attach "before the main"...Correct? As well as the section from the IRC I posted...? In which case you would not see it in the panel.....? See exhibit 250.8 in 2017 handbook...
 