• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Service question

SCBO1

Platinum Member
Joined
Oct 28, 2009
Messages
4,349
Location
MID WEST
Do you allow a service drop for a main panel from the POCO to go to an accessory building (detached garage) and then feed the main structure (House)?

Is it permitted by code to do it this way or is this an AHJ call?

What I have been told is the POCO charges more per kilowatt when doing it this way?
 
Where is the service disconnect? The service disconnect can be on a detached garage.....or as is common here, on an ADU. In farm country it can be on a pole by the road....but hey now, we are California.
 
Last edited:
Existing residential home and their adding a detached garage. The house service is underground and is under the proposed garage, so they want to place the main panel in the garage and feed the house from the garage panel.
 
Nothing in the code would not allow this. But of coarse the utility company has rules too. Here you need to get permission of the location for the service from the utility company first.
 
Agree nothing in the code prevents that setup, can go either way. We have two electrical utilities in our neck of the woods, one requires you just to poke out the SEC out of the meter socket (aerial or underground service lateral) and the other the electrician installs to the aerial drop from the service lateral at the weather head
 