I got this question today; and am not sure I understand. This is for a building accessory to two others. It's a large church. "Existing service #1 has 1200A and 400A service disconnects. Existing service #2 has 200A, 200A, 200A, 300A service disconnects. Our plan is to add two more 400A disconnects to the existing service #2 if the utility company can handle the additional load on the existing service conductors/transformer. Our decision is based on the following NEC criteria.
NEC 230.2©(1): We are allowed to have two services since our total ampacity will be 3,300 amps.
NEC 230.40 Exception No. 2: We are allowed to have a single set of service conductors supplying up to (6) grouped disconnects.
NEC 230.71: We are allowed to have up to (6) disconnects grouped together per service.
This is all the information I have. 2011 NEC; Thanks, Uncle Bob
NEC 230.2©(1): We are allowed to have two services since our total ampacity will be 3,300 amps.
NEC 230.40 Exception No. 2: We are allowed to have a single set of service conductors supplying up to (6) grouped disconnects.
NEC 230.71: We are allowed to have up to (6) disconnects grouped together per service.
This is all the information I have. 2011 NEC; Thanks, Uncle Bob