gtyler75
REGISTERED
Referencing 2015 Michigan Building Code in relation to an R-2 building
Trying to maximize the possibilities of a single-exit R-2 building. So looking at Section 1006 Number of Exits
In particular, I'm looking at the single exit exceptions (1006.3.2)- if any of the conditions apply, a story is allowed a single exit. I see one small, but potentially consequential, discrepancy within these exceptions.
1006.3.2 Condition 1 references a table specific to R-2 occupancies that allows a single exit for basement, first, second, and third floors (max 4 dwelling units per floor, 125 ft common path of egress travel). It also says 4th or higher story dwelling units are not permitted with a single exit.
1006.3.2 Condition 2, however, does not have the upper story caveat. Instead, it says that an R-2 space/area (dwelling unit) with a max occupancy load of 10 and common egress travel distance of 125 ft is allowed a single exit.
It seems very possible to have dwelling units on the fourth, or maybe higher floors, that would meet Condition 2, but would obviously conflict with Condition 1. I know they are technically not co-dependent, but I'm just wondering if anyone has tried this, or guidance on whether I'd run into issues later on.
Many thanks
Trying to maximize the possibilities of a single-exit R-2 building. So looking at Section 1006 Number of Exits
In particular, I'm looking at the single exit exceptions (1006.3.2)- if any of the conditions apply, a story is allowed a single exit. I see one small, but potentially consequential, discrepancy within these exceptions.
1006.3.2 Condition 1 references a table specific to R-2 occupancies that allows a single exit for basement, first, second, and third floors (max 4 dwelling units per floor, 125 ft common path of egress travel). It also says 4th or higher story dwelling units are not permitted with a single exit.
1006.3.2 Condition 2, however, does not have the upper story caveat. Instead, it says that an R-2 space/area (dwelling unit) with a max occupancy load of 10 and common egress travel distance of 125 ft is allowed a single exit.
It seems very possible to have dwelling units on the fourth, or maybe higher floors, that would meet Condition 2, but would obviously conflict with Condition 1. I know they are technically not co-dependent, but I'm just wondering if anyone has tried this, or guidance on whether I'd run into issues later on.
Many thanks