jar546
CBO
When you have to size a supply side bonding jumper as required in NEC 250.102, you would use Table 250.102(C)(1) which is based on the size of the largest ungrounded conductor. The table is easy to use. For example, if the largest ungrounded conductor entering the enclosure is 250MCM then you would need a 2awg copper bond wire. If you had parallel conductors, such as 3 sets of 250MCM then you would add them together, 250x3=750MCM and the bond size would be a 2/0 copper.
BUT, what if you had a 400A service with 2 sets of 3/0 copper. How would you do the math?
BUT, what if you had a 400A service with 2 sets of 3/0 copper. How would you do the math?