steveray
SAWHORSE
Maybe....but hey....If the BO accepts it, it must be good....Most of their stuff that needs engineering says so in the ESR....Like helical piers...Is ICC trying to subvert your states licensing laws?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Maybe....but hey....If the BO accepts it, it must be good....Most of their stuff that needs engineering says so in the ESR....Like helical piers...Is ICC trying to subvert your states licensing laws?
I reread a bit more of GBA article and author - the builder - said he'd never had a code issue, on several such builds. No interior load bearing walls (plenum trusses to ease air handling) and floor easily supports 40 psf live load. I'm leaning toward thinking this complies prescriptivly with the IRC.
R104.9 Approved materials and equipment. Materials,
equipment and devices approved by the building official shall
be constructed and installed in accordance with such approval.
The code is a compilation of criteria with which materials,
equipment, devices and systems must comply to
be suitable for a particular application. The building
official has a duty to evaluate such materials, equipment,
devices and systems for code compliance and,
when compliance is determined, approve the same for
use. The materials, equipment, devices and systems
must be constructed and installed in compliance with,
and all conditions and limitations considered as a
basis for, that approval. For example, the manufacturer’s
instructions and recommendations are to be followed
if the approval of the material was based even in
part on those instructions and recommendations.
The approval authority given the building official is a
significant responsibility and is a key to code compliance.
The approval process is first technical and then
administrative and must be approached as such. For
example, if data to determine code compliance are
required, such data should be in the form of test
reports or engineering analysis and not simply taken
from a sales brochure.
What prescription in the IRC for floor systems does this "slabless" slab fail to satisfy? I.e. what code section would one cite to fail such an installation?How? "Prescriptively" means the code "prescribes" it.
It's a slab on ground floor. I can't find anyplace in the 2028 IRC that specifies what that slab is. Not defined and Merriam Webster says: a thick plate or slice (as of stone, wood, or bread). It supports the required loads of chapter 3. It meets or exceeds the insulation requirements. Foam is used on grade and required by IRC. Maybe not suitable where termites of any nationality are an issue but the subject is in northern Minnesota and I'm in northern NY. Termites not an issue. Moisture protection is addressed. Wood floors on ground are even addressed in the IRC.How? "Prescriptively" means the code "prescribes" it. This system isn't addressed at all in the IRC, or the IBC. IMHO it can't comply "prescriptively." The building official has the authority to accept such a system on his/her own iniative, if he/she is willing to assume the risk.
The Commentary, however, reminds us that we should not exercise this authority lightly:
What is the risk that the building official would accept? I understand that if the building official acts in accordance with his authority, which includes code compliance. he has governmental immunity. What risk does a building official have if he has governmental immunity.
Section R504 Pressure Preservative-Treated Wood Floors (On Ground)
R504.1 General
Pressure preservative-treated wood basement floors and floors on ground shall be designed to withstand axial forces and bending moments resulting from lateral soil pressures at the base of the exterior walls and floor live and dead loads. Floor framing shall be designed to meet joist deflection requirements in accordance with Section R301.
R504.1.1 Unbalanced Soil Loads
Unless special provision is made to resist sliding caused by unbalanced lateral soil loads, wood basement floors shall be limited to applications where the differential depth of fill on opposite exterior foundation walls is 2 feet (610 mm) or less.
R504.1.2 Construction
Joists in wood basement floors shall bear tightly against the narrow face of studs in the foundation wall or directly against a band joist that bears on the studs. Plywood subfloor shall be continuous over lapped joists or over butt joints between in-line joists. Sufficient blocking shall be provided between joists to transfer lateral forces at the base of the end walls into the floor system.
R504.1.3 Uplift and Buckling
Where required, resistance to uplift or restraint against buckling shall be provided by interior bearing walls or properly designed stub walls anchored in the supporting soil below.
R504.2 Site Preparation
The area within the foundation walls shall have all vegetation, topsoil and foreign material removed, and any fill material that is added shall be free of vegetation and foreign material. The fill shall be compacted to ensure uniform support of the pressure preservative-treated wood floor sleepers.
R504.2.1 Base
A minimum 4-inch-thick (102 mm) granular base of gravel having a maximum size of 3/4 inch (19.1 mm) or crushed stone having a maximum size of 1/2 inch (12.7 mm) shall be placed over the compacted earth.
R504.2.2 Moisture Barrier
Polyethylene sheeting of minimum 6-mil (0.15 mm) thickness shall be placed over the granular base. Joints shall be lapped 6 inches (152 mm) and left unsealed. The polyethylene membrane shall be placed over the pressure preservative-treated wood sleepers and shall not extend beneath the footing plates of the exterior walls.
R504.3 Materials
Framing materials, including sleepers, joists, blocking and plywood subflooring, shall be pressure-preservative treated and dried after treatment in accordance with AWPA U1 (Commodity Specification A, Special Requirement 4.2), and shall bear the label of an accredited agency.
I don't know about all of this... I mean what is the POINT? To me, I would venture to guess this is a lot more costly than having a concrete slab?
I was told that it was fairly reasonable on cost compared to a traditional concrete SoG. Time to construct was much faster; can put the slab down and frame walls same day, no concrete curing. And then there is the energy efficiency (R-20 continuous is what I saw).I don't know about all of this... I mean what is the POINT? To me, I would venture to guess this is a lot more costly than having a concrete slab?
Thanks for this post. Kind of what I was thinking.I've worked through permitting two of these composite wood-SoG floors. My understanding is that they are quite common in Europe, particularly in the northern regions where thermal performance is an important design element.
While the IRC does not spell out exactly how to construct these floors, the principles of construction are direct enough that I fully believe that these floors can be permitted under the IRC. We already, predominantly through the energy codes, require foam under concrete slabs. Placed WSP directly on top of this foam, the sheathing has no span and is continuously supported. Using T&G floor sheathing, double layered, the floor is rigid and joints are supported. From a risk standpoint, I think we all see termite/pests as a risk - although, that is location specific and readily mitigated. Risk of collapse or structural failure is less than that with a wood framed floor.
And beyond what I have noted, keep in mind that the IRC already includes PPT Wood Floors on Ground (2021 IRC Sec. 504).