I found the article in this month's NFPA Journal about the NFPA 13 Small Room Rule interesting and it does help clarify a sometimes confusing rule, but I am still stuck on one question. The rule allows the head to be no more than 9' from a single wall within a room 800 sq ft or less, but how do you measure that? Is it a straight line to the walls or should you also measure diagonally to the corners of the room?
Case in questions: I have a tenant renovation in progress, light-hazard office 2900 sq ft total with offices approximately 9.5' x 14' (133 sq ft). They are using the small room rule in these rooms, and if measured in a straight line they are a max of 8' from a single wall BUT, when measuring from the head to the corners they are about 10' 6" from the center of the sprinkler head. Is this allowed?
Thanks.
Case in questions: I have a tenant renovation in progress, light-hazard office 2900 sq ft total with offices approximately 9.5' x 14' (133 sq ft). They are using the small room rule in these rooms, and if measured in a straight line they are a max of 8' from a single wall BUT, when measuring from the head to the corners they are about 10' 6" from the center of the sprinkler head. Is this allowed?