chris kennedy
Sawhorse
If a bedroom has two doors, is a smoke alarm required outside of each door?
Thanks
Thanks
I agree....cda said:With out seeing a floor plan, I would say yes
So the bedroom has two entrances ??chris kennedy said:Master bedroom has a door into the living room and another into a hall. This is a remodel with a designer. He doesn't want one outside the bedroom in the living room. I have one in the hall.Which code art addresses this?
See Section R314.3 [ `12 & `15 IRC ].+ & +" Which code art addresses this? "
R314.3 Location.north star said:+ & +See Section R314.3 [ `12 & `15 IRC ].
No !........Typically, the alarms are installed in the Hallways [ i.e. - the mostcommon MOE from those sleeping areas ], ...where the audible alarm can"Do you put one in the bathroom/ which would be another entrance to the bedroom ??"
Ok using thatnorth star said:+ $ +No !........Typically, the alarms are installed in the Hallways [ i.e. - the most
be heard throughout the structure \ floor.
From Kidde User Guidecda said:Do you put one in the bathroom/ which would be another entrance to the bedroom ??
""""AVOID"""rogerpa said:From Kidde User Guide2. LOCATIONS TO AVOID
Smoke alarms should not be installed within 3 ft (.9m) of the following:
the door to a kitchen, the door to a bathroom containing a tub or shower,
forced air supply ducts used for heating or cooling,
ceiling or whole house ventilating fans, or other high air flow
areas.
I read this to say, not IN the bathroom either.
Which one has a higher ceiling?Master bedroom has a door into the living room and another into a hall.
Actually from that wording I would think that you could ahve a POT that is 41 feet maximum with a single detector placed in the middle?mark handler said:NATIONAL FIRE PROTECTION ASSOCIATION NFPA 72
11.5.1......outside of each separate dwelling unit sleeping area, within 21ft of any door to a sleeping room, the distance measured along a path of travel.
So is the outside POT to the bedrooms two entrances within 21 ft??
And if the two doors empty into two different parts of the house ??mtlogcabin said:Which one has a higher ceiling?The purpose of the smoke detector is to detect smoke. It's location should be determined by where it will function the best in the event of a fire.
Yep ........JPohling said:Actually from that wording I would think that you could ahve a POT that is 41 feet maximum with a single detector placed in the middle?
As they say since it is football seasonchris kennedy said:If a bedroom has two doors, is a smoke alarm required outside of each door?Thanks
There is other verbiage that requires them to be in close proximity to the bedroom door. 41 feet, IMHO is not in close proximity.JPohling said:Actually from that wording I would think that you could ahve a POT that is 41 feet maximum with a single detector placed in the middle?
Actually 42 feetmark handler said:There is other verbiage that requires them to be in close proximity to the bedroom door. 41 feet, IMHO is not in close proximity.