Smoke ratings and corridors

Michael Brown

SAWHORSE
Joined
Mar 27, 2017
Messages
38
Location
Covington, GA
Is a conditioned corridor in a multifamily building required to be smoke rated? 3 story, 12 unit building with a single stairwell to the ground level.
 
They have to be fire rated per 1020.2 and 420.2.

1020.2 Construction

Corridors shall be fire-resistance rated in accordance with Table 1020.2. The corridor walls required to be fire-resistance rated shall comply with Section 708 for fire partitions.
Exceptions:

  1. A fire-resistance rating is not required for corridors in an occupancy in Group E where each room that is used for instruction has not less than one door opening directly to the exterior and rooms for assembly purposes have not less than one-half of the required means of egress doors opening directly to the exterior. Exterior doors specified in this exception are required to be at ground level.
  2. A fire-resistance rating is not required for corridors contained within a dwelling unit or sleeping unit in an occupancy in Groups I-1 and R.
  3. A fire-resistance rating is not required for corridors in open parking garages.
  4. A fire-resistance rating is not required for corridors in an occupancy in Group B that is a space requiring only a single means of egress complying with Section 1006.2.
  5. Corridors adjacent to the exterior walls of buildings shall be permitted to have unprotected openings on unrated exterior walls where unrated walls are permitted by Table 705.5 and unprotected openings are permitted by Table 705.8.

420.2 Separation Walls

Walls separating dwelling units in the same building, walls separating sleeping units in the same building and walls separating dwelling or sleeping units from other occupancies contiguous to them in the same building shall be constructed as fire partitions in accordance with Section 708.
 