• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Solar etc.

Span

Registered User
Joined
Nov 2, 2009
Messages
95
Location
CA
Solar installation needs to follow 120% rule per NEC 705.12 used to be 690.64. I've just learned from my BO yesterday, it does not apply to center feed main breaker panel, it only apply to top or bottom feed main breaker.

He told me 50% of cities OK for both type and 50% are not. Anyone have information regarding why center feed main breaker can not use 120% rule?
 