• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Some Thoughts/Questions About Covered Mall Buildings

texasbo

Platinum Member
Joined
Jan 4, 2010
Messages
1,059
I haven't done a new mall since we were under the UBC, and hadn't really kept up with the changes that much, so some of this may sound ignorant, so I apologize in advance.

What benefit do you get for having an "anchor building"? In other words, unless a tenant is more than 3 stories, why not just call all buildings mall tenant spaces? You get to eliminate rated separations between the mall and the space, whereas if it were an "anchor building", it would require either a fire wall or a fire barrier. You could still have exterior access to the space, and all you would have to do is have a required exit for 1 person into the covered mall for it not to be an "anchor".

Does anyone find it interesting that you can have an unlimited area type IIB A-2 if it's part of a mall?

Is anyone aware of why the smoke control provisions were removed, except for atria within malls?
 
Texasbo: Boy what a great question!!!! As to the last statement YES! If you look closely smoke control did go away.

For the other questions I will need to spend some time on them.
 
syarn: exactly; calling it an anchor building, with rquired exits completely independent of the mall, allows you to not impose any additional occupant load into the covered mall building. However, if you design the anchor building exits such that a very minimal occupant load exits into the mall, then you can call it a tenant instead of an anchor, you can still have exterior entrances/exits, and you are not imposing appreciable occupant load on the mall. Best of all, you can avoid separation requirements.
 
cda said:
Sometimes anchor stores are not owned by the mall??
I'd say more often than not, at least around here, they are under separate ownership.
 
Some history first.

After the Plymouth Meeting Mall fire in 1970, the various code communities took action to change the codes to address what was at the time a fairly new type of design. The fire started in one tenant space and then progressed out, into the mall and toward the large anchor store at the end. There was no requirement for alarms, sprinklers, standpipes or other fire safety systems that today we take for granted. They basically threw the book at malls adding everything that could be thought of as a way to make these facilities safer - the typical knee-jerk reaction. Interestingly, the anchor store had a type of a sprinkler system at the mall entrance and the fire stopped its progression as soon as it hit that water. To be sure, this was not willy-nilly. The Board for the Coordination of the Model Codes (BCMC) deliberated and decided on a position to present to the three code groups (and NFPA). Of course, each group decided on something slightly different.

Over the years, BOCA had slowly whittled a number of the requirements away from the mall provisions. Smoke control would be based on the atrium provisions since that is when a "hole-in the floor" becomes a problem. Anchors could be things besides mercantile since theaters and even hotels were being added to malls. Fires in facilities built under those "altered" provisions substantiated the fact that the main thing was sprinklers. After that it was all about warning folks and then assisting the fire departments in doing their tasks.

When the three codes unified, there was plenty of compromise. Smoke control control for one-story malls was back in based on the fact that two out of three of the legacy organizations had it in there. Somehow voice alarms was added - above the simple fire alarm provisions in two of the three. Sprinklers and standpipes were the same. Then, after the I-codes were published, the smoke control section started to change to reflect what the BOCA people had been telling us - smoke in one-story malls is not manageable. Smoke in two story spaces is questionable and difficult at best to manage. It takes a height of at least 30-60 feet to be able to manage smoke to some degree. Even the Life Safety Code does not require smoke control for one-story malls.

As for anchors; the main reason to be an anchor is to have independent control of the entrances to the facility, irrespective of the mall's operating hours. An anchor can have midnight madness sales long after the mall is closed. Because of that, its exits must be counted separately from those in the mall. Also, as a result of the separate ownership, there must be a rated separation between the mall and the anchor. Under the BOCA this was a fire wall (with its structural Independence and all that). Under Southern it wasn't clear what it was. Under UBC it was simply a rated wall. The compromise was to use the rated wall in most cases.

If the anchor is no more than three-stories, then it could be a tenant space except for the separate ownership concern. Anything with taller expectations needs to be an anchor.

<<< btw: Riddle me this Batman: Why is a three-story 85,000 SF per story department store of unrated construction OK as long as it's attached to the mall (assuming it has all the sprinklers and bells included); but, if the mall is demolished it is now too big? Hmmm? >>>
 
Your last question is exactly what I'm getting at; there is stuff that is just senseless in the mall provisions. You could have an 85K, 3 story department store, with no separation whatsoever from the mall, if just 1 occupant exited into the mall from the department store. You could also have an unlimited, non-rated A-2, with no separation whatsoever from the mall. Tear the mall down, and they are both illegal.
 
texasbo said:
Your last question is exactly what I'm getting at; there is stuff that is just senseless in the mall provisions. You could have an 85K, 3 story department store, with no separation whatsoever from the mall, if just 1 occupant exited into the mall from the department store. You could also have an unlimited, non-rated A-2, with no separation whatsoever from the mall. Tear the mall down, and they are both illegal.
So, either one set of provisions is too lenient or the other is too restrictive. Who's gonna make that call?
 