Split bolts for GECs

jar546

CBO
Joined
Oct 16, 2009
Messages
12,938
Location
Not where I really want to be
Does anyone actually check the manufacturer's spec for split bolts to determine whether or not they meet the requirements of 250.64(D)(1) with the new changes from 05 to 08?

I love the main trunk line with taps method for connecting GECs of multiple disconnects but prefer to see exothermic welds or irreversible compression fittings.

Thoughts?
 
Re: Split bolts for GECs

Ilsco and Burndy copper split bolts are a listed mechanical connector for grounding.
 
Re: Split bolts for GECs

dcspector said:
Ilsco and Burndy copper split bolts are a listed mechanical connector for grounding.
Correct, most of the copper or bronze split bolts that I see are listed for grounding and bonding connections.

Chris
 