spray booth question, but building code related
cda
LIFETIME SAWHORSE
Basement
since a pre fab spray booth is not an "H" occupancy, is there a square foot size, that would require two doors out of one???
IFC 2003
1504.1.2.4 Means of egress. Means of egress shall be
provided in accordance with Chapter 10.
Exception: Means of egress doors from
premanufactured spray booths shall not be less than
30 inches (762 mm) in width by 80 inches (2032 mm)
in height.
2006 IFC, I think it may be section 1014.1 in 2003 IFC if memory serves me right................
1015.1 Exit or exit access doorways required. Two exits or
exit access doorways from any space shall be provided where
one of the following conditions exists:
1. The occupant load of the space exceeds the values in
Table 1015.1.
2. The common path of egress travel exceeds the limitations
of Section 1014.3.
3. Where required by Sections 1015.3, 1015.4 and 1015.5.
Exception: Group I-2 occupancies shall comply with Section
1014.2.2.
TABLE 1015.1
SPACES WITH ONE MEANS OF EGRESS
OCCUPANCY MAXIMUM OCCUPANT LOAD
A, B, Ea, F, M, U 49
H-1, H-2, H-3 3
H-4, H-5, I-1, I-3, I-4, R 10
S 29
a. Day - Spaces with one exit.....
A spray booth is an appliance and I've never classified a spray booth as a Group H-2 occupancy. I have classified spray rooms as H-2s when the amount in storage exceeds the MAQ.
For the purposes of M.O.E., I classify spray booths as Industrial Spaces under the "Function of Space" provision in 2009 IFC Table 1004.1.1, which equates to an occupant load of 100 square feet gross/person. Applying Table 1015.1, a second exit access opening wouldn't be required until 49 people could occupy the booth. I've never seen more than 5 people in a booth at any one time and I've never seen 49, even in an educational setting.