• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Sprinklers on Branch Line

tmurray

SAWHORSE
Joined
Jun 10, 2011
Messages
3,028
Location
NB, Canada
Hello all,

I'm review and updating a course for our local building officials association and have run into a problem. The test asks what the maximum number of sprinklers per branch line is. The old test said there was a maximum of 8 based on clause 14.5.2.1.1 of NFPA 13-2002. I'm updating the code references and cannot find similar provisions in the 2007. Any help would be appreciated.

Thanks,

Trevor
 
That would have to be in the pipe schedule system section, hydraulically calculated may have many especially gridded systems see 22.5.2.1 for the 8 requirement and the exceptions in 2007 NFPA 13
 