D
DwightB
Guest
2006 IBC:
I'm working with a church, so dealing with A-3 occupancy. Section [F] 903.2.1 says for Group A occupancy says "automatic sprinkler system SHALL be provided ... throughout the floor area where Group A is located...and all floors from the Group A occupancy to and including the level of exit discharge".
This seems to cover any and all occurrences. I don't see the need for [F] 903.2.1.3 which adds "automatic sprinkler system shall be provided for Group A-3 where ONE of the following conditions exist: 1. The fire area exceeds 12,000 sf. Note: The previous paragraph already said "THROUGHOUT ALL FLOORS of Group A", so this was already covered. 2. The fire area has an occupant load of 300 or more. Note: The previous paragraph already said "THROUGHOUT ALL FLOORS of Group A", so this also was already covered. 3. The fire area is located on a floor other than a level of exit discharge serving such occupancies. Note: The previous paragraph already said "in all floors from the Group A occupancy to and including the nearest level of exit discharge serving the Group A occupancy", so this also was already covered.
So my question is: If [F] 903.2.1 already covered ALL situations, why did they specify in [F] 903.2.1.3 that there are special situations where a special need exists?
I'm working with a church, so dealing with A-3 occupancy. Section [F] 903.2.1 says for Group A occupancy says "automatic sprinkler system SHALL be provided ... throughout the floor area where Group A is located...and all floors from the Group A occupancy to and including the level of exit discharge".
This seems to cover any and all occurrences. I don't see the need for [F] 903.2.1.3 which adds "automatic sprinkler system shall be provided for Group A-3 where ONE of the following conditions exist: 1. The fire area exceeds 12,000 sf. Note: The previous paragraph already said "THROUGHOUT ALL FLOORS of Group A", so this was already covered. 2. The fire area has an occupant load of 300 or more. Note: The previous paragraph already said "THROUGHOUT ALL FLOORS of Group A", so this also was already covered. 3. The fire area is located on a floor other than a level of exit discharge serving such occupancies. Note: The previous paragraph already said "in all floors from the Group A occupancy to and including the nearest level of exit discharge serving the Group A occupancy", so this also was already covered.
So my question is: If [F] 903.2.1 already covered ALL situations, why did they specify in [F] 903.2.1.3 that there are special situations where a special need exists?