Stack washer and dryer ?
SCBO1
MID WEST
I have a commercial restaurant project that the owner wants to install a residential type stack-able W&D. 2012IMC Section 504.3 requires a clean-out.
The HVAC contractor has told the GC that he will have to install a booster fan at an additional cost if a clean-out has to be installed. The 4-inch duct will go up and out the exterior wall approximately 18 feet.
Do you think the HVAC contractor is correct that a booster fan will need to be installed?
pc1
504.3 Cleanout.
Each vertical riser shall be provided with a means for cleanout.
And if you disconnect at the unit and run a brush up the vent line,
That does not count ?
PC,
The booster fan application was approved for use in some previous editions of the
IMC,...however, ...the actual booster fan components were found to be non-United
States compliant........The allowing of the booster fans went away in the `06 I-Codes.
I am unsure as to whether or not they are actually allowed today.......Even if
they are, ...are the booster fan components approved for use in the U.S. ?
Pcinspector1 said:
I have a commercial restaurant project that the owner wants to install a residential type stack-able W&D. 2012IMC Section 504.3 requires a clean-out. The HVAC contractor has told the GC that he will have to install a booster fan at an additional cost if a clean-out has to be installed. The 4-inch duct will go up and out the exterior wall approximately 18 feet.
pc1
504.8
10. A cleanout opening shall be located at the base of the shaft to provide access to the duct to allow for cleaning and inspection. The finished opening shall be not less than 12 inches by 12 inches (305 mm by 305 mm).
The dryer manufactures installation instructions should provide the info for permitted length of the exhaust run, Does not matter if it is horizontal or vertical. The clean-out is required if a booster fan is used or not.
I agree, need the manufactures install instructions, may not need a booster fan at all, but 504.3 VERTICAL rise requires the cleanout.
Section 504.3 requires a means for cleanout. IMHO, that is not the same thing as a cleanout. Disconnecting the transition duct could be a means for cleanout for a single dryer. GPE.
pc1
I hate vertical runs but allowed
Did you look at all the bends and stuff ;;
504.6.4 Duct length.
The maximum allowable exhaust duct length shall be determined by one of the methods specified in Section 504.6.4.1 or 504.6.4.2.
504.6.4.1 Specified length.
The maximum length of the exhaust duct shall be 35 feet (10 668 mm) from the connection to the transition duct from the dryer to the outlet terminal. Where fittings are used, the maximum length of the exhaust duct shall be reduced in accordance with Table 504.6.4.1.
north star said:
PC,
Booster fans are back in as of 2015. See 504.5 IMC (or M1502.4.4 IRC) Dryer exhaust duct power ventilators. Power ventilators must meet UL 705 - 04 with revisions thru March 2012. http://codes.iccsafe.org/app/book/content/2015-I-Codes/2015%20IMC%20HTML/CHAPTER%205.html
I concur georgia. Also, cleanouts and booster fans do not trigger requirements for the other. I would be curious as to where that HVAC contractor received their information.
As if my job is'nt already tough enough code interpretation: From the web:
I read a mechanical code that indicated a "cleanout" was required in the clothes dryer exhaust. What does that mean?
Answer Correct, the new "International Mechanical Code" specifically states on "Section 504.3 Cleanout - Every vertical riser shall be provided with a means of cleanout." The intent of this code element is to provide an accessible means to remove the lint accumulation that would fall vertically (settle) to a low spot in the vertical run. If a means already exist to access this, (i.e., the usual ell through the drywall or a Dryerbox) then a cleanout is not required. Our engineers' professional opinion is that The Dryerbox meets the requirements as a cleanout opening for the dryer exhaust system.