NYS code, not sure what it says, but if based off of ifc
check 315.3 2009 IFC
315.3 Outside storage. Outside storage of combustible materials
shall not be located within 10 feet (3048 mm) of a property
line.
Exceptions:
1. The separation distance is allowed to be reduced to 3
feet (914 mm) for storage not exceeding 6 feet (1829
mm) in height.
2. The separation distance is allowed to be reduced
when the fire code official determines that no hazard
to the adjoining property exists.
315.3.1 Storage beneath overhead projections from
buildings. Where buildings are protected by automatic
sprinklers, the outdoor storage, display and handling of
combustible materials under eaves, canopies or other projections
or overhangs is prohibited except where automatic
sprinklers are installed under such eaves, canopies or other
projections or overhangs.
315.3.2 Height. Storage in the open shall not exceed 20 feet
(6096 mm) in height.
315.4 Storage underneath high-voltage transmission lines.
Storage located underneath high-voltage transmission lines
shall be in accordance with Section 316.5.2.
some may argure that the IFC does not apply to a house
not much in fire code to cover this, a man's home is his wood pile,
do you have a code enforcement dept?? sometimes they have rules on outside strorage.