Tim Mailloux
REGISTERED
165K sf Elementary school project in CT, 2018 CT code (amended 2015 IBC), type 2B construction, 2 stories with sprinklers……
Due to the size of the building footprint we had to chop it up into (5) individual zones using 2 hour rated fire walls. The fire walls are structurally independent cast in place concrete. At two locations we have enclosed exit stairs adjacent to the fire walls, with the fire wall making up (1) of the (4) sides of the exit enclosure. The contractor would like to embed some steel plates into the fire wall pour to attach the upper & intermediate stair landing to. The. Generally we don’t like to attach anything to fire walls, however in this case I can sort of get onboard with it.
Due to the size of the building footprint we had to chop it up into (5) individual zones using 2 hour rated fire walls. The fire walls are structurally independent cast in place concrete. At two locations we have enclosed exit stairs adjacent to the fire walls, with the fire wall making up (1) of the (4) sides of the exit enclosure. The contractor would like to embed some steel plates into the fire wall pour to attach the upper & intermediate stair landing to. The. Generally we don’t like to attach anything to fire walls, however in this case I can sort of get onboard with it.