Mech
REGISTERED
IBC 2009
Type IIIB Construction
B, S-1, S-2 mixed occupancy, unseperated, unsprinklered
How many stairs do I need from a 2nd level parts storage area at a car dealership? I'm not sure yet if this will be a mezzanine or a second story. If 2 stairs are required, does one of them need to be enclosed or can they both be unenclosed? The occupant load is less than 10 and the common path of travel will be less than 75 ft from the most remote point of the 2nd level down to the ground floor. You can disregard accessibility requirements for now. That issue will be addressed under a separate thread.
709.2 Exception 16 says I may not need an enclosure.
1016.1 Exception 3 seems to indicate that I need two stairs, one of which can be unenclosed.
1022.1 Exception 1 says the staircase does not need to be enclosed if the occupant load is less than 10 and the design complies with Item 1.1 or 1.2, which it does.
I am thinking that I only need one stairs, which can be unenclosed, from the upper level that I can call a second story.
Below are the code sections that I referenced above.
Thanks in advance.
708.2 Shaft enclosure required. Openings through a floor/ceiling assembly shall be protected by a shaft enclosure complying with this section.
Exceptions:
11. A shaft enclosure shall not be required for floor openings created by unenclosed stairs or ramps in accordance with Exception 3 or 4 in Section 1016.1.
16. Where permitted by other sections of this code.
1016.1 Travel distance limitations. Exits shall be so located on each story such that the maximum length of exit access travel, measured from the most remote point within a story along the natural and unobstructed path of egress travel to an exterior exit door at the level of exit discharge, an entrance to a vertical exit enclosure, an exit passageway, a horizontal exit, an exterior exit stairway or an exterior exit ramp, shall not exceed the distances given in Table 1016.1.
Exceptions:
3. In other than occupancy Groups H and I, the exit access travel distance to a maximum of 50 percent of the exits is permitted to be measured from the most remote point within a building to an exit using unenclosed exit access stairways or ramps when connecting a maximum of two stories. The two connected stories shall be provided with at least two means of egress. Such interconnected stories shall not be open to other stories.
SECTION 1022 EXIT ENCLOSURES
1022.1 Enclosures required. Interior exit stairways and interior exit ramps shall be enclosed with fire barriers constructed in accordance with Section 707 or horizontal assemblies constructed in accordance with Section 712, or both. Exit enclosures shall have a fire-resistance rating of not less than 2 hours where connecting four stories or more and not less than 1 hour where connecting less than four stories. The number of stories connected by the exit enclosure shall include any basements but not any mezzanines. Exit enclosures shall have a fire-resistance rating not less than the floor assembly penetrated, but need not exceed 2 hours. Exit enclosures shall lead directly to the exterior of the building or shall be extended to the exterior of the building with an exit passageway conforming to the requirements of Section 1023, except as permitted in Section 1027.1. An exit enclosure shall not be used for any purpose other than means of egress.
Exceptions:
1. In all occupancies, other than Group H and I occupancies, a stairway is not required to be enclosed when the stairway serves an occupant load of less than 10 and the stairway complies with either Item 1.1 or 1.2. In all cases, the maximum number of connecting open stories shall not exceed two.
1.1. The stairway is open to not more than one story above its level of exit discharge; or
1.2. The stairway is open to not more than one story below its level of exit discharge.
Type IIIB Construction
B, S-1, S-2 mixed occupancy, unseperated, unsprinklered
How many stairs do I need from a 2nd level parts storage area at a car dealership? I'm not sure yet if this will be a mezzanine or a second story. If 2 stairs are required, does one of them need to be enclosed or can they both be unenclosed? The occupant load is less than 10 and the common path of travel will be less than 75 ft from the most remote point of the 2nd level down to the ground floor. You can disregard accessibility requirements for now. That issue will be addressed under a separate thread.
709.2 Exception 16 says I may not need an enclosure.
1016.1 Exception 3 seems to indicate that I need two stairs, one of which can be unenclosed.
1022.1 Exception 1 says the staircase does not need to be enclosed if the occupant load is less than 10 and the design complies with Item 1.1 or 1.2, which it does.
I am thinking that I only need one stairs, which can be unenclosed, from the upper level that I can call a second story.
Below are the code sections that I referenced above.
Thanks in advance.
708.2 Shaft enclosure required. Openings through a floor/ceiling assembly shall be protected by a shaft enclosure complying with this section.
Exceptions:
11. A shaft enclosure shall not be required for floor openings created by unenclosed stairs or ramps in accordance with Exception 3 or 4 in Section 1016.1.
16. Where permitted by other sections of this code.
1016.1 Travel distance limitations. Exits shall be so located on each story such that the maximum length of exit access travel, measured from the most remote point within a story along the natural and unobstructed path of egress travel to an exterior exit door at the level of exit discharge, an entrance to a vertical exit enclosure, an exit passageway, a horizontal exit, an exterior exit stairway or an exterior exit ramp, shall not exceed the distances given in Table 1016.1.
Exceptions:
3. In other than occupancy Groups H and I, the exit access travel distance to a maximum of 50 percent of the exits is permitted to be measured from the most remote point within a building to an exit using unenclosed exit access stairways or ramps when connecting a maximum of two stories. The two connected stories shall be provided with at least two means of egress. Such interconnected stories shall not be open to other stories.
SECTION 1022 EXIT ENCLOSURES
1022.1 Enclosures required. Interior exit stairways and interior exit ramps shall be enclosed with fire barriers constructed in accordance with Section 707 or horizontal assemblies constructed in accordance with Section 712, or both. Exit enclosures shall have a fire-resistance rating of not less than 2 hours where connecting four stories or more and not less than 1 hour where connecting less than four stories. The number of stories connected by the exit enclosure shall include any basements but not any mezzanines. Exit enclosures shall have a fire-resistance rating not less than the floor assembly penetrated, but need not exceed 2 hours. Exit enclosures shall lead directly to the exterior of the building or shall be extended to the exterior of the building with an exit passageway conforming to the requirements of Section 1023, except as permitted in Section 1027.1. An exit enclosure shall not be used for any purpose other than means of egress.
Exceptions:
1. In all occupancies, other than Group H and I occupancies, a stairway is not required to be enclosed when the stairway serves an occupant load of less than 10 and the stairway complies with either Item 1.1 or 1.2. In all cases, the maximum number of connecting open stories shall not exceed two.
1.1. The stairway is open to not more than one story above its level of exit discharge; or
1.2. The stairway is open to not more than one story below its level of exit discharge.