We use the 2018 IRC for houses here which does not have the exception no matter if the sunroom is screened in or weather tight.
E3901.2 General purpose receptacle distribution. In every
kitchen, family room, dining room, living room, parlor,
library, den, sun room, bedroom, recreation room, or similar
room or area of dwelling units, receptacle outlets shall be
installed in accordance with the general provisions specified in
Sections E3901.2.1 through E3901.2.3 (see Figure E3901.2).
But we need to make sure that it is a sunroom, but I'm not sure if a sun room is the same as a sunroom:
[RB] SUNROOM. A one-story structure attached to a dwelling
with a glazing area in excess of 40 percent of the gross
area of the structure’s exterior walls and roof.
For the definition applicable in Chapter 11, see Section
N1101.6.
So if it has less than 40% glazing or no glazing at all it's not a sunroom.
(My dictionary says glazing is the act of installing windows????)
So how do you measure the glazing area? IRC says:
[RB] GLAZING AREA. The interior surface area of all
glazed fenestration, including the area of sash, curbing or
other framing elements, that enclose conditioned space.
Includes the area of glazed fenestration assemblies in walls
bounding conditioned basements.
So if the sunroom is not conditioned or not attached to a dwelling you can't add up the glass or plastic sq ft to see if it is over 40%. This means if it is not conditioned it can't be a sunroom even if it is all glass, so you don't need to space the receptables as a sun room per code.
Also this would mean a Category 1 sunroom is not a sunroom. Maybe it's a porch?
Porch in not defined in the IRC but my dictionary it says it's a covered shelter in front of a building. (Notice, not on the side or rear of a building)
IRC E3901.7 requires at least one receptacle on a porch not higher then 6'-6" above the porch surface. According to my dictionary a porch wall, roof, window, or windowsill is a surface.
I hope this makes it plan.