• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Stairwell storage

Vlab20

Bronze Member
Joined
Mar 11, 2010
Messages
89
Location
Midwest
I have a 3 story Institutional building...I-2. Hospital on stories 1 and 2 and Skilled Nursing Facility on 3rd floor. Due to the elderly patients on the 3rd floor the staff have available multiple "evacuation" chairs that can seat a patient and is used to traverse a stairwell. This chair is built to go down the stairs. The staff wants to store the chair on the top landing inside the stairwell. The chair folds up and can securely mount to the wall. The chair in this position would not interfere with the required egress width of the stair.

As I read NFPA 101 2000 edition...current hospital/nursing home code in our state...

Stairs

7.2.2.5.3* Usable Space. There shall be no enclosed, usable

space within an exit enclosure, including under stairs, nor

shall any open space within the enclosure be used for any purpose

that has the potential to interfere with egress.

Does anyone have any thoughts or experience with a situation like this. I have a call into the AHJ. Thanks
 
( ~ ) = ( ~ )

No experience with your application, but my initial thought is...

"Why store it in the stairwell, when IMO, it seems it would be

more readily accessible inside the Skilled Nursing Facility

itself.

FWIW, ...I would not desire to have it stored in the stairwell.

Too easy for it to be used for other purposes, or to "become

missing".

Also, ...it is common for more than the minimum egress widths

to be needed, especially in a emergency situation [ EX:

emergency response personnel going up and floor occupants

going down. ].

( ~ ) = ( ~ )
 
I guess what prompted this question is the head of facilities wants to locate them in the stairwell because during a recent drill the staff could not find them when they were stored inside the skilled space. Now the obvious solution is to train the staff and to keep these special chairs in a special place. The skilled nursing space has limited storage capacity and thus is a challenge to designate a space for these special evac chairs.
 
( ~ ) = ( ~ )

Then my question would be, ..."What makes anyone think that they

will be able to find them in a stairwell ?"

Establish a place within the S.N.F., ...train the staff [ if possible ],

...place legible signs on that space, and have the staff sign an

acknowledgment statement, rather than add stuff to a stairwell. :eek:

[ i.e. - require the staff to actually be responsible within their own

spaces ].



( ~ ) = ( ~ )
 
Mounting the egress chairs in the area of rescue assistance is pretty common as that will let the fire department find them when they are confronted with a wheelchair bound person in the 3rd floor landing.
 
Sounds good as long as not in exit width and will not cause problem with door swing

No area on wall prior to stair door, inside skilled area?
 
The space just outside of the stairwell can't work. This is one of those very old buildings and just not enough storage space properly positioned for today's uses. I will let you know what the AHJ says.
 
steveray said:
I do not believe I would have an issue with what you describe....the chairs are for egress...they can be in the exit....IMO
Problem is the employees than take advantage and besides the med carts, food carts, cleaning carts you find a few more things
 
You might throw out I think a few FD pre stage hose packs in the stairwells
 
Is there sufficient space to build a fire rated compartment on the top landing to house the chairs? The chairs would no longer be in the stairwell.

We just made a compartment on the ground floor of a stair tower to isolate a sump pump. That compartment is now the safest part of the building; it has 2 hour fire rated walls and ceiling, with fire suppression!
 
Can't enclose a space per the NFPA Section cited...

"7.2.2.5.3* Usable Space. There shall be no enclosed, usable

space within an exit enclosure, including under stairs, nor

shall any open space within the enclosure be used for any purpose

that has the potential to interfere with egress."

However the last part is the key. The storage of these chairs will actually enhance, not interfere with, egress IMHO.
 
Thanks JBI. I forgot an important part of the sump pump scenario - access to the sump pump was from outside the stair tower. The Dept of Health plan reviewer ruled that the new fire rated walls and ceiling removed the sump pump / usable space from the stair tower.
 
Does that stick out more than 4"? I have had them take plumbing cleanouts out of stairwells at plan review (wasn't my fault they were already installed)....I do not think I would have an issue with that chair if it was an acceptable protrusion...
 