Attached garage, when requiring gyp protection of framing members due to living space above, do you require steel beans to also be wrapped?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Code calls for one 5/8" type X on structural members supporting space above. How do you get several layers?ICE said:Yes and probably several layers.
I ask for it.Yankee said:Code calls for one 5/8" type X on structural members supporting space above. How do you get several layers?
Was it called out in code as one hour separation, , , ever?mark handler said:Some departments are still requiring one hour separation/protection in garages.One layer of 1/2" or 5/8" does not provide that
I'm sure you say "please" also : )ICE said:I ask for it.
Yes under the old [1997] UBC, minimum 5/8-inch Type X gypsum board on walls and two layers on lidYankee said:Was it called out in code as one hour separation, , , ever?
As I remember it, you needed a one hour separation between between Group R, Division 3 and Group U. there was an exception that allowed the wall to have the 5/8" gyp to be applied to only to the garage side wall. But one layer on a horizontal plane does not provide one hour, thus you needed two layers on the horizontal plane [lid].fatboy said:Really? I don't recollect the two layers on lids. Was that a CA amendment to the UBC? I don't have my 97 UBC at home........
yes, when habitable space was aboveRider Rick said:Mark,Was it two layers of 5/8" Type X on the lid?
. . . . yes, I know, thanks for the link. Did the previous code call for a "one hour floor/ceiling assembly", or for "two layers of gyp"?mark handler said:there are one hour floor ceiling assemblieshttp://www.thebuildingcodeforum.com/forum/fire-links/7301-ga-600-2009-fire-resistance-design-manual.html
GA FILE NO. FC 5406
As I posted before It called for a one hour separation, you cannot achieve that with one layer.Yankee said:. . . . yes, I know, thanks for the link. Did the previous code call for a "one hour floor/ceiling assembly", or for "two layers of gyp"?
2001 CBC based on the 1997 UBCpete_t said:Only one layer of 5/8 was required on the garage side. 2001 CBC
302.4 See also Section 504.6.1.
Exceptions:
3. In the one-hour occupancy separation between Group R, Divi-
sions [for SFM] 2.1, 2.2, 2.2.1 and 3 and Group U Occupancies, the
separation may be limited to the installation of materials approved for
one -hour fire-resistive construction on the garage side