that is accessibility, see 1010.1.5Yes. Not an occupied space therefore not required to be accessible.
1103.2.9 Equipment spaces.
Spaces frequented only by service personnel for maintenance, repair or occasional monitoring of equipment are not required to comply with this chapter.
Thank you both for your repliesthat is accessibility, see 1010.1.5
Yep missed that my apologiesUnless it is more than just a Fire Sprinkler Riser Room then Exception #6 would be applicable.
Exceptions:
6. Doors serving equipment spaces not required to be accessible in accordance with Section 1103.2.9 and serving an occupant load of five or less shall be permitted to have a landing on one side to be not more than 7 inches (178 mm) above or below the landing on the egress side of the door.
Awesome, thanks!Unless it is more than just a Fire Sprinkler Riser Room then Exception #6 would be applicable.
Exceptions:
6. Doors serving equipment spaces not required to be accessible in accordance with Section 1103.2.9 and serving an occupant load of five or less shall be permitted to have a landing on one side to be not more than 7 inches (178 mm) above or below the landing on the egress side of the door.