Step at Fire Riser Room

Yes. Not an occupied space therefore not required to be accessible.

1103.2.9 Equipment spaces.
Spaces frequented only by service personnel for maintenance, repair or occasional monitoring of equipment are not required to comply with this chapter.
 
2015 IBC

1010.1.5 Floor Elevation​

Diagram
There shall be a floor or landing on each side of a door. Such floor or landing shall be at the same elevation on each side of the door. Landings shall be level except for exterior landings, which are permitted to have a slope not to exceed 0.25 unit vertical in 12 units horizontal (2-percent slope).

some exceptions do not seem to apply
 
Yes. Not an occupied space therefore not required to be accessible.

1103.2.9 Equipment spaces.
Spaces frequented only by service personnel for maintenance, repair or occasional monitoring of equipment are not required to comply with this chapter.
that is accessibility, see 1010.1.5
 
Unless it is more than just a Fire Sprinkler Riser Room then Exception #6 would be applicable.

Exceptions:

6. Doors serving equipment spaces not required to be accessible in accordance with Section 1103.2.9 and serving an occupant load of five or less shall be permitted to have a landing on one side to be not more than 7 inches (178 mm) above or below the landing on the egress side of the door.
 
Unless it is more than just a Fire Sprinkler Riser Room then Exception #6 would be applicable.

Exceptions:

6. Doors serving equipment spaces not required to be accessible in accordance with Section 1103.2.9 and serving an occupant load of five or less shall be permitted to have a landing on one side to be not more than 7 inches (178 mm) above or below the landing on the egress side of the door.
Yep missed that my apologies
 
Unless it is more than just a Fire Sprinkler Riser Room then Exception #6 would be applicable.

Exceptions:

6. Doors serving equipment spaces not required to be accessible in accordance with Section 1103.2.9 and serving an occupant load of five or less shall be permitted to have a landing on one side to be not more than 7 inches (178 mm) above or below the landing on the egress side of the door.
Awesome, thanks!
 