Mech
REGISTERED
2009 IBC
Can a stepped building fire wall terminate 30 inches above the upper roof per 706.6 instead of complying with section 706.6.1?
My scenario has an approximate 4 - 5 foot difference in roof heights.
Thanks in advance.
706.6 Vertical continuity. Fire walls shall extend from the foundation to a termination point at least 30 inches (762 mm) above both adjacent roofs.
Exceptions:
1. Stepped buildings in accordance with Section 706.6.1.
2. Not applicable to scenario
3. Walls shall be permitted to terminate at the underside of noncombustible roof sheathing, deck or slabs where both buildings are provided with not less than a Class B roof covering. Openings in the roof shall not be located within 4 feet (1220 mm) of the fire wall.
4. Not applicable to scenario
5. Not applicable to scenario
706.6.1 Stepped buildings. Where a fire wall serves as an exterior wall for a building and separates buildings having different roof levels, such wall shall terminate at a point not less than 30 inches (762 mm) above the lower roof level, provided the exterior wall for a height of 15 feet (4572 mm) above the lower roof is not less than 1-hour fire-resistance-rated construction from both sides with openings protected by fire assemblies having a fire protection rating of not less than 3/4 hour.
Exception: Where the fire wall terminates at the underside of the roof sheathing, deck or slab of the lower roof, provided:
1. The lower roof assembly within 10 feet (3048 mm) of the wall has not less than a 1-hour fire-resistance rating and the entire length and span of supporting elements for the rated roof assembly has a fire-resistance rating of not less than 1 hour.
2. Openings in the lower roof shall not be located within 10 feet (3048 mm) of the fire wall.
Can a stepped building fire wall terminate 30 inches above the upper roof per 706.6 instead of complying with section 706.6.1?
My scenario has an approximate 4 - 5 foot difference in roof heights.
Thanks in advance.
706.6 Vertical continuity. Fire walls shall extend from the foundation to a termination point at least 30 inches (762 mm) above both adjacent roofs.
Exceptions:
1. Stepped buildings in accordance with Section 706.6.1.
2. Not applicable to scenario
3. Walls shall be permitted to terminate at the underside of noncombustible roof sheathing, deck or slabs where both buildings are provided with not less than a Class B roof covering. Openings in the roof shall not be located within 4 feet (1220 mm) of the fire wall.
4. Not applicable to scenario
5. Not applicable to scenario
706.6.1 Stepped buildings. Where a fire wall serves as an exterior wall for a building and separates buildings having different roof levels, such wall shall terminate at a point not less than 30 inches (762 mm) above the lower roof level, provided the exterior wall for a height of 15 feet (4572 mm) above the lower roof is not less than 1-hour fire-resistance-rated construction from both sides with openings protected by fire assemblies having a fire protection rating of not less than 3/4 hour.
Exception: Where the fire wall terminates at the underside of the roof sheathing, deck or slab of the lower roof, provided:
1. The lower roof assembly within 10 feet (3048 mm) of the wall has not less than a 1-hour fire-resistance rating and the entire length and span of supporting elements for the rated roof assembly has a fire-resistance rating of not less than 1 hour.
2. Openings in the lower roof shall not be located within 10 feet (3048 mm) of the fire wall.