I am looking at a condition that involves a new building proposed on an urban site, with one wall being an existing party wall along one property line. The existing building on the adjacent property is two stories. The proposed new building will be 5 stories. The designer believes that the stepped building provisions of 706.6.1 will permit them to reduce the fire rating of the exterior wall on the shared lot line and provide window openings at the upper floors. I believe that notwithstanding the provisions of 706.6.1, the exterior wall of the new building above the party wall must also comply with Sections 602 and 705 based on fire separation distance (which, in this case, means no exterior openings permitted). Is this correct? Or does the designer have a legitimate argument?
Just for an academic argument - would this also apply if we were looking at two separated buildings on the same lot, i.e., does the imaginary lot line then extend above the lower separated building - which would then seem to make Section 706.6.1 moot?
(Note the code jurisdiction uses 2018 IBC)
Just for an academic argument - would this also apply if we were looking at two separated buildings on the same lot, i.e., does the imaginary lot line then extend above the lower separated building - which would then seem to make Section 706.6.1 moot?
(Note the code jurisdiction uses 2018 IBC)