Still an Atrium with louvers on roof?

blugosi

SAWHORSE
Joined
Sep 25, 2018
Messages
121
Location
Greece
I am reviewing a modification of an existing building, where a high bay storage area of a mercantile occupancy is transformed to two stories business (60+60 thousand square feet) with an atrium in the middle.
The architects want to bypass atrium requirements per NFPA/IBC by having some kind of louvers on the roof.
I am not convinced. This is vague and the mere existence of louvers does not seem enough to say this opening is not an atrium.
What do you think?
 
What requirement do they think the louvers will satisfy?
They claim that smoke will not be trapped or something to that effect.o_O
I believe that the fundamental parameter to address atria in a special manner is free movement of air between compartments, as well as smoke accumulation on high floors, especially on tall atria.
 
Section 404.5, Exception 1: "In other than Group I-2, and Group I-1, Condition 2, smoke control is not required for atriums that connect only two stories."
 
Section 404.5, Exception 1: "In other than Group I-2, and Group I-1, Condition 2, smoke control is not required for atriums that connect only two stories."
Thank you Ron,

Requirements for an Atrium are not limited to the smoke control provision I think. First I want to be clear on the definition.
 