Structural requirements for Storages Racks
Papio Bldg Dept
Papillion
I know there is a section of the IBC (I am using the 2006, but 2009 references are just as helpful) that dictates at a certain point when storage racks need to be anchored and/or engineered for their design loads, but I am not able to find the section. Having a case of the Mondays. Any help is appreciated. Thanks in advance.
2009 IBC
1707.5 Storage racks and access floors.
Periodic special inspection is required during the anchorage of access floors and storage racks 8 feet (2438 mm) or greater in height in structures assigned to Seismic Design Category D, E or F.
2208.1 Storage racks.
The design, testing and utilization of industrial steel storage racks made of cold-formed or hot-rolled steel structural members, shall be in accordance with the RMI/ANSI MH 16.1. Where required by ASCE 7, the seismic design of storage racks shall be in accordance with the provisions of Section 15.5.3 of ASCE 7, except that items (1), (2) and (3) of Section 15.5.3 of ASCE 7 do not apply when the rack design satisfies RMI/ANSI MH 16.1.
Builder Bob said:
1613.1 of the 2006 IBC ---- redirects you to ASCE-07
Thanks BB. 15.5 NONBUILDING STRUCTURES SIMILAR TO BUILDINGS, 15.5.3, Steel Storage Racks is what I was having trouble finding. I thought there was something specifically in the IBC, Chapter 16, that mentioned Storage Racks, but that appears to be only referencing the ASCE 7 in several sections, including the one you listed. Thanks again.
mtlogcabin said:
2009 IBC1707.5 Storage racks and access floors.
The language is a little bit different in the 2006, but essentially the same. Thanks again for your quick response. Good to know I wasn't seeing things.