• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Stud Penetration >40%

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,055
Location
Somewhere Too Hot & Humid
These studs are doubled to support the weight from some of the roof load above on this normally non-load bearing wall. Stud shoes needed:

IMAG0236-1.jpg


View above:

IMAG0237-1.jpg
 
The stud is doubled, so even on an interior bearing partition a stud shoe would not be required if the hole bored was greater than 40%.

The issue I believe I see is the bearing stud is bored over 60% and would require an approved stud shoe to correct the overboring.
 
  • Like
Reactions: JBI
The studs are doubled already in order to support the weight from above. They are load bearing and are bored well in excess of the 40% maximum. Simpso shoes or equivalent are required.
 
jar546 said:
The studs are doubled already in order to support the weight from above. They are load bearing and are bored well in excess of the 40% maximum. Simpso shoes or equivalent are required.
add a stud to the left of the hot water pipe and one to the right of the 2" vent/drain pipe and who cares how many holes you put in the 2 studs. they become na with the new studs, or go for the stud shoes if that's your pleasure!
 
Top plate need a strap. It appears to be a bearing wall.

The double stud could be handle as pwood said or have a stud shoe. By placing a stud next to the hot water line the double has no purpose, unless some type of load is above.
 
And they used the cheap vent connector for the bath fan. 14' max. I agree with requiring the shoe. Most shoes also require mini lag bolts not nails or screws.
 
60% is the maximum! Stud shoe is NOT a fix. The stud shoe is allowed as an alternative to doubling the stud if bored between 40% and 60% in a bearing wall. The non bearing requirement is 60% maximum with no provisions for greater than 60%. They need to use the poper bit for the pipe size not one bit for the whole job! With that said we have allowed a stud shoe on one NON BEARING stud only when bored over 60%, i.e. the washer box requires a 2" drain and it can prove difficult to fit everything into a 14" space so that is our "compromise" if you will. When the washer box is in a bearing wall we require 2x6 or a second wall inside to hold the plumbing. That works well for most because they frame it up about 5' and trim the top with a shelf behind the washer and dryer, big plus for most.

Second, I think the strap on the top plate is only required for a notch. So in therory, one could drill a 3" hole in the middle of the top plate, leaving a 1/4" of wood on either side and not require a strap. Right? They would have to cut the face of the plate before a strap is required I believe.
 
I always understood that stud plates performed a 2 fold function. One was to prevent screws and nails from penetrating what was behind them as well adding to "what was missing" (reinforceing) no?
 
codeworks said:
I always understood that stud plates performed a 2 fold function. One was to prevent screws and nails from penetrating what was behind them as well adding to "what was missing" (reinforceing) no?
Not your typical nail plates......code says something about a strap with 8 sikes on each side....funny thing is it seems that you can take the whole top plate out (or at least multiple sections) as long as the strap can clear 8 spikes either side....that one always has sat a little funny with me...haven't seen it pushed and don't know if it is even possible....but some ugly wording IMHO...
 
codeworks said:
I always understood that stud plates performed a 2 fold function. One was to prevent screws and nails from penetrating what was behind them as well adding to "what was missing" (reinforceing) no?
As steveray stated the regular "nail plate" is just that, a plate to stop nail penetration and protect what is behind. The structural strap I was refering to is the one required by 2009 IRC R602.6.1 Drilling and notching of top plate ...metal tie not less than 16Ga and 1 1/2 " wide shall be fastened across and to the top plate at each side with not less than eight 10d nails having a min. length of 1 1/2" ...

TYPICAL NAIL PLATE

attachment.php


STRUCTURAL STRAP - required by R602.6.1

attachment.php


The "stud shoe" will help support "what is missing" but wraps around the stud.

STUD SHOE

attachment.php
 
Last edited by a moderator:
  • Like
Reactions: JBI
codeworks said:
Use 2x6 walls for plumbing walls. Becomes less of an issue.
Agree 100%

I don't think I have seen a plumbing wall that is not built with 2x6 any more guess the building got tired of fix over bores
 
[quote=Buelligan washer box requires a 2" drain and it can prove difficult to fit everything into a 14" space so that is our "compromise" if you will. When the washer box is in a bearing wall we require 2x6 or a second wall inside to hold the plumbing.

you do know that you can space studs at 24" o.c.?
 
Also, 5X8 oversized plates are required at plate penetrations for plumbing. These can substitute for the required structural strap if plate has been severely notched.
 
pwood said:
[quote name=Buelligan washer box requires a 2" drain and it can prove difficult to fit everything into a 14" space so that is our "compromise" if you will. When the washer box is in a bearing wall we require 2x6 or a second wall inside to hold the plumbing. you do know that you can space studs at 24" o.c.?
YES, and why we felt one overbored stud with a stud shoe was probably equivalant. The plumbers likes the trap arm in a stud for the extra support.
 
Buelligan said:
60% is the maximum! Stud shoe is NOT a fix. The stud shoe is allowed as an alternative to doubling the stud if bored between 40% and 60% in a bearing wall. The non bearing requirement is 60% maximum with no provisions for greater than 60%. They need to use the poper bit for the pipe size not one bit for the whole job! With that said we have allowed a stud shoe on one NON BEARING stud only when bored over 60%
I like this position. If you look at the ES report there is a table of load values the stud shoes will support. Granted this is outside the prescriptive avenues, but I think a little discretion could justify that the stud shoe is adequate for minor variations from the prescriptive requirements (especially-- as pointed out-- when you could frame 24" oc)
 
Sorry for bumping an old thread, but as this also is related to a thread/question I had for a similar situation...


60% is the maximum! Stud shoe is NOT a fix. The stud shoe is allowed as an alternative to doubling the stud if bored between 40% and 60% in a bearing wall..."

The 2015 IRC R602.6 appears to have been updated, or at least that's how I'm reading it... It seems to be worded now that a stud shoe is an exception to notching/cutting or boring greater than 60%, regardless of other details. Meaning notching/cutting of studs greater than 25% of it's width, as well as recognition of doubling studs when drilled/bored between 40-60% of the member's width (and limited to (2) successive doubling of studs), are both or all allowed to be resolved with an "approved" stud shoe, installed per manufacturer's recommendations.

Am I reading that right? Or has there been clarification on this somewhere that differs?

Thanks
 