Sulphuric acid storage
mjesse
Lincolnshire, IL.
Looking to find information regarding "approved" construction methods or designs for control areas in accordance with IFC 2703.11.
Business has multiple pallets of 108-6 qt. boxes of sulphuric acid for lead-acid batteries.
I am envisioning a 6" concrete curb on a concrete slab, lined with an epoxy coating. How do I evaluate the "liquid-tightness" of such an assembly?
Next question, when multiple control areas are required due to maximum loading limits, can separation be provided by a 1 hr. barrier wall, or say 100' physical separation, or is it necessary to have a fully enclosed "room" for separation.
Local FD is involved in acceptance of design proposal, I would just like to be a little more educated on the subject.
Thanks,
mj
which fire code and edition is this under??
and when you say business what type??
FORGOT to ask if spinkled building???
so if I do my college educated math correctly
one of these pallets has 162 gallons???
without sprinklers:
he can have 975 gallons just setting there or 6.01851852 of these pallets???
and if sprinkled 12.037037 pallets???
soo how many does he have or want????????????????
yes you can use the self contained pallets as on the web link above
please if I did the math wrong somone correct my paper
CDA, yes, fully sprinklered.
I agree 975 gallons unless sprinkled, then 100% increase = 1950 gallons.
They want 6200+ gallons.
If I am interpreting correctly, they may have up to 4 containment areas of 1950 each (7800 max. gal.) IF they are separated by 1 hr fire walls, I should have been more specific in my first post in asking if a fire barrier (single plane wall) is permissible as separation between containment areas, or is each area to be fully "enclosed" in a 1 hr. room.
Alternately, would anyone make a compromise if a separation distance of X feet was provided in lieu of a fire wall.
Thanks.
just make a portion of the building an "H" and get it over with, that way they do not have to worry about quantity, and more then likely cheaper.
suggest get and FPE involved and also might save some money
does not appear seperation gets you anything
CONTROL AREA. Spaces within a building which are enclosed
and bounded by exterior walls, fire walls, fire barriers
and roofs, or a combination thereof, where quantities of hazardous
materials not exceeding the maximum allowable quantities
per control area are stored, dispensed, used or handled.
414.2 Control areas. Control areas shall be those spaces
within a building where quantities of hazardous materials not
exceeding the maximum quantties allowed by this code are
414.2.1 Construction requirements. Control areas shall
be separated from each other by not less than a 1-hour fire
barrier constructed in accordance with Chap ter 7.
If they make it an H (H-4) you have to check type of construction, height and area, mechanical code, etc. Don't forget IBC 415 if H-4.
Thanks all.
Looks like I'm heading in the right direction.
Will require fire separation and secondary containment per the Group S, or....Give them the opportunity to have the building evaluated (on their dime) to see if the construction qualifies for H-4.
mj
CDA, I would think so.
I would request some sort of 3rd party review evaluation of the existing building stating that it meets the requirements of H-4.
What that means as far as floor/wall/roof construction, I don't know.....yet.
Livin' and learnin',
mj