Mr. Inspector
We are just adopting the 2015 which sends you to AAMA/NPEA/NSA 2100 for sunrooms and just looking over it I have a few concerns.
3.2.19 SUNROOM: A one-story structure attached to a dwelling with a glazing area in excess of 40 percent of the gross area of the structure’s exterior walls and roof. (same as the IRC definition)
4.0 SUNROOM CATEGORIES
4.1 The following categories are used to specify differing criteria for sunrooms based on their intended use. Performance specifications vary by sunroom category with stated minimum requirements. The room definitions are intended to provide required features for that classification of sunroom. Additional or optional features added to enhance the performance of the sunroom product are not within the scope of this standard.
4.1.1 Category I
A Thermally Isolated Sunroom with walls that are either open or enclosed with insect screening or 0.5 mm (20 mil) maximum thickness plastic film. Category I shall meet the structural requirements as outlined in Section 6.0. The space is defined as a non-habitable, non-conditioned sunroom.
Question 1. Category I has does not fit the definition of a Sunroom because it has no glazing. Does this mean we go back to the IRC code for this category? I would call this a porch.
8.2 FOUNDATIONS
8.2.1 Concrete Foundations
Load bearing walls supporting no more than one floor level and roof in all Sunroom Categories shall be permitted to be supported by a concrete foundation of no less than 200 mm (12 in) in width provided that foundation is supported by a continuous footing that meets the criteria of Section 8.2.3.
8.2.2 Slab on Grade
Where permitted by the local jurisdiction and in areas with a frost line depth of zero as specified by the building official, sunrooms shall be permitted to be supported on a concrete slab on grade provided that the slab is not less than 90 mm (3.5 in) thick, and does not support a concentrated load in excess of 340 kg (750 lbs) per column.
8.2.3 Slab on Grade with Turn-Down Footing
Unless otherwise allowed in this specification, all Sunrooms in areas with a frost line depth of zero shall be permitted to be supported on a concrete slab on grade with a turn-down footing. The turn down footing shall support the bearing walls and load carrying elements of the structure.
All Sunrooms in areas with a frost line depth greater than zero shall be permitted to be supported on a concrete slab on grade with a turn-down perimeter footing in accordance with the requirements of the local building code.
8.2.4 Decks Supporting Sunrooms
All Categories of Sunrooms shall be permitted to be supported on a deck that is constructed in accordance with the requirements of the local building code.
Question 2. Does this mean if you build a sunroom you can't build it on piers unless you build it on a treated wood deck?
8.6.2 Receptacle Outlets
Receptacle outlets in Category IV and V sunrooms shall be installed in accordance with NFPA 70 Article 314.
EXCEPTION 3: Category I, II and III sunrooms are exempt from requirements for receptacle outlets.
Question 3. Don't you think it's odd that receptacle outlets are not required in Category I, II and III sunrooms but porches, decks and balconies are required to have receptacles in the IRC?
4.1.1 Category I
8.2 FOUNDATIONS
8.2.2 Slab on Grade