Doing a rough-in inspection and came across a white switch box making contact with a B-vent flue. First thought was you can't do that! So I have been trying to find if it is permitted?

The 1-inch clearance for the B-vent flue is to combustibles. If this box was non-metallic or Bakelite would it be allowed to touch the flue?

What about if the box was PVC? I would think this would not be allowed.
 
The NEC would probably require high-temperature insulation on conductors and possibly oversizing the conductors for a high ambient temperature.

Hopefully the manufacturers instructions require separation from B-vents and other high temperature items.
 
Allied Moulded #434 Fiberglas switch box touching a 1-inch clearance B-vent.

  • Standards:
    ANSI / UL 514C: File No. E30594

    UL-Logo-250x332.jpg
  • Fire Classification:
    Fire Test of Building Construction Materials
    ANSI / UL 263: File No. CEYY.R9379 (Category / File No.)

    Note: Products must also be certified to: ANSI / UL 514C

    Fire Resistance Classification in Wall Assemblies 2-Hours or less
    Shall be separated by a horizontal distance of not less than 24 inches

    Note: For more details please refer to the UL fire resistive directory and Allied Moulded’s CEYY.9379 (Outlet boxes and fittings classified for fire resistance)
 