jar546
CBO
Condo High-Rise
Existing switchgear from 1958 needs to be replaced, as per the engineer and the electrical contractor. No parts available, gear won't turn off.
The existing location does not meet NEC 110.26(A) for workspace.
The existing location is now too low for the FEMA FIRMS as the BFE has changed over the decades.
The new gear can't be raised high enough to be compliant.
The new gear can't be installed in a way that complies with NEC 110.26(A)
The electrical room where the existing switchgear/service disconnects are is on the other side of the POCO vault, so the location of the electrical room is critical.
What do you do as the AHJ? There is a floodplain ordinance/FEMA rule that can't be complied with, along with an NEC compliance issue.
Existing switchgear from 1958 needs to be replaced, as per the engineer and the electrical contractor. No parts available, gear won't turn off.
The existing location does not meet NEC 110.26(A) for workspace.
The existing location is now too low for the FEMA FIRMS as the BFE has changed over the decades.
The new gear can't be raised high enough to be compliant.
The new gear can't be installed in a way that complies with NEC 110.26(A)
The electrical room where the existing switchgear/service disconnects are is on the other side of the POCO vault, so the location of the electrical room is critical.
What do you do as the AHJ? There is a floodplain ordinance/FEMA rule that can't be complied with, along with an NEC compliance issue.