Greetings to everyone!

I have a "new" medical clinic type facility in the plan review stage. On the plans, in each

restroom the plans show a postive pressure rather than a negative pressure (i.e - there

is more Supply Air coming in to each room than there is Exhaust Air going out).

QUESTION # 1: Is there somewhere in the IMC or the IECC, or ASHRAE 90.1 that

requires the system to be balanced (equal air in, ..equal air out), or as I have been taught,

in the restrooms, there should be a negative pressure effect (a vacuum effect) so as to

effectively remove any noxious odors?

As usual, no RDP has designed these submittals.

Thanks for your input!

.
 
globe trekker said:
Greetings to everyone!I have a "new" medical clinic type facility in the plan review stage. On the plans, in each

restroom the plans show a postive pressure rather than a negative pressure (i.e - there

is more Supply Air coming in to each room than there is Exhaust Air going out).

QUESTION # 1: Is there somewhere in the IMC or the IECC, or ASHRAE 90.1 that

requires the system to be balanced (equal air in, ..equal air out), or as I have been taught,

in the restrooms, there should be a negative pressure effect (a vacuum effect) so as to

effectively remove any noxious odors?

As usual, no RDP has designed these submittals.

Thanks for your input!

.
Just as in your bathroom scenario for negative along with lockerrooms etc. In medical applications certain rooms are required to be positive to keep contaminants out of the space.
 
IMC 501.3

"... Where mechanical exhaust isrequired in a room or space in other than occupancies in R-3

and dwelling units in R-2, such space shall be maintained with a

neutral or negative pressure. If a greater quantity of air is supplied

by a mechanical ventilating supply system than is

removed by a mechanical exhaust for a room, adequate means

shall be provided for the natural or mechanical exhaust of the

excess air supplied. ..."
 