2006 IBC, Section 712 - Penetrations.
Please confirm my thinking here is correct -
Background:
This is for an EXISTING building, single story, unsprinklered Type IIIB building currently housing F2 and B occupancies.
I am re-purposing the building to house S1/B/F1 occupancies. Per AHJ amended requirements, this increase in occupancy hazard causes a need for this building to comply with current code (IBC 2006 with City of Houston amendments).
The total GSF floor area is 14,400 GSF, so I must sprinkler or compartmentalize the fire areas. I chose to compartmentalize, since the area of town is older, and I'm not sure that pressure exists to install a new sprinkler system, even if the owner could afford it.
I have designed a 3 -hr. steel stud and gypsum board fire barrier wall (UL U419) to split the fire area into (1) 10,900 SF area and (1) 3,400 SF area.
My question:
Is about FIRESTOPS.
My question concerns the lack of a T-rating in thru-wall penetrations and joints that surround the 3 hour wall. I have two types of penetrants: 1/2" conduit with 12 AWG copper conductors and 1" dia steel pipe carrying gas supply for radiant heaters.
This section is broken down into two conditions: 712.3 FIRE RESISTANT RATED WALLS and 712.4 HORIZONTAL ASSEMBLIES
And after digging through all that, it seems that NO t-rating is required on thru-penetration firestops for walls. Floors, yes, but not walls. Is there any condition that could require a t-rating on a wall penetration firestopping system?
Does one exist in the 2012 code?
Thanks in advance.
Please confirm my thinking here is correct -
Background:
This is for an EXISTING building, single story, unsprinklered Type IIIB building currently housing F2 and B occupancies.
I am re-purposing the building to house S1/B/F1 occupancies. Per AHJ amended requirements, this increase in occupancy hazard causes a need for this building to comply with current code (IBC 2006 with City of Houston amendments).
The total GSF floor area is 14,400 GSF, so I must sprinkler or compartmentalize the fire areas. I chose to compartmentalize, since the area of town is older, and I'm not sure that pressure exists to install a new sprinkler system, even if the owner could afford it.
I have designed a 3 -hr. steel stud and gypsum board fire barrier wall (UL U419) to split the fire area into (1) 10,900 SF area and (1) 3,400 SF area.
My question:
Is about FIRESTOPS.
My question concerns the lack of a T-rating in thru-wall penetrations and joints that surround the 3 hour wall. I have two types of penetrants: 1/2" conduit with 12 AWG copper conductors and 1" dia steel pipe carrying gas supply for radiant heaters.
This section is broken down into two conditions: 712.3 FIRE RESISTANT RATED WALLS and 712.4 HORIZONTAL ASSEMBLIES
And after digging through all that, it seems that NO t-rating is required on thru-penetration firestops for walls. Floors, yes, but not walls. Is there any condition that could require a t-rating on a wall penetration firestopping system?
Does one exist in the 2012 code?
Thanks in advance.