Table 110.26(A)(1) Exposed live parts.

Joined
Oct 24, 2009
Messages
1,554
Location
Miami Fla
I have a situation where I have two 460V AC units on a pad with 40" separation between them. So my question is about 'Condition 3'. What constitutes 'exposed live parts'? Both covers would have to be open for this condition to exist. I would say that this falls under condition 2, although the clearance doesn't meet that requirement either. :roll:

Thank you.
 
Re: Table 110.26(A)(1) Exposed live parts.

I would say that you have conditions 3 as you have the potential for exposed live parts on both sides.

Condition 2 would be live parts on one side and a grounded surface such as concrete, brick or tile walls on the other side.

Chris
 
Re: Table 110.26(A)(1) Exposed live parts.

raider1 said:
I would say that you have conditions 3 as you have the potential for exposed live parts on both sides.
I have always been of this opinion also, but as I was getting ready to fire off a RFI today I realized it is not clearly defined in the NEC.
 