• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Table 506.2 Per Floor or Total?

Phil B

SAWHORSE
Joined
Sep 15, 2018
Messages
130
Location
Florida
I am looking for a clear statement that confirms whether or not the values in Table 506.2 for Allowable Areas are per floor or total. Years ago it was clear, not so anymore.
 
This is per story.

There may be a better example of where this is stated somewhere else, but Equation 5-2 has a note that says "No individual story shall exceed the allowable area as determined by Equation 5-2." For context, Equation 5-2 is the calculation for the allowable area of a single-occupancy multistory building, and it states that no story should exceed the allowable area per Table 506.2 multiplied by the frontage increase factor.
 
I am looking for a clear statement that confirms whether or not the values in Table 506.2 for Allowable Areas are per floor or total. Years ago it was clear, not so anymore.
It may be helpful if you focus on how Table 506.2 is only presenting the value At to be used in the various equations in Chapter 5. It’s the equation that is used to determine the area of the building - which could be a single floor or multiple floors. But the equations also have the frontage increase which can increase the Table 506.2 area by as much as 0.75 of the non-sprinklered area (per Equation 5-5 in the 2018 IBC,) so depending on the siting of the building the area of a single-story building will be more than the value found in Table 506.2.
 
Than
It may be helpful if you focus on how Table 506.2 is only presenting the value At to be used in the various equations in Chapter 5. It’s the equation that is used to determine the area of the building - which could be a single floor or multiple floors. But the equations also have the frontage increase which can increase the Table 506.2 area by as much as 0.75 of the non-sprinklered area (per Equation 5-5 in the 2018 IBC,) so depending on the siting of the building the area of a single-story building will be more than the value found in Table 506.2.
Thank you all for your input!
 