Does this exception include Unprotected, Nonsprinklered (UP, NS) where openings are not permitted?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Is it permitted to have 25% unprotected openings in all three conditions at 3 to 5?Footnote "d" applies to a 3 to 5 foot fire separation distance
Footnote "f" is for over a 5 foot fire separation distance
It's optional and required as applicable.Code anticipates R's to be sprinkled??
Thanks for understanding my question.Footnote "d" allows only R-3 occupancies to have a total combined protected and unprotected openings of 25% between 3 & 5 foot fire separation distances
Footnote "f" allows all protected and unprotected opening in R-3 occupancies to be unlimited in size if the fire separation distance is greater than 5 feet
f. The area of unprotected and protected openings shall not be limited for Group R-3 occupancies, with a fire separation distance of 5 feet or greater.
And this interpretation for R-3 aligns with openings not limited greater than 5 ft.