Francis Vineyard
REGISTERED
2009 IBC; R-2 less than 5 ft. from Type 2 non-sprinklered open parking structure on same lot.
Does there need to be a zero fire-resistant wall to block the openings only on the side of the open parking structure less than 10 ft. adjacent to the lot line?
TABLE 705.8
g. The area of openings in an open parking structure with a fire separation distance of 10 feet or greater shall not be limited.
406.3.7 Fire separation distance. Exterior walls and openings
in exterior walls shall comply with Tables 601 and 602.
The distance to an adjacent lot line shall be determined in
accordance with Table 602 and Section 705.
TABLE 602 d. Open parking garages complying with Section 406 shall not be required to have a fire-resistance rating.
Francis
Does there need to be a zero fire-resistant wall to block the openings only on the side of the open parking structure less than 10 ft. adjacent to the lot line?
TABLE 705.8
g. The area of openings in an open parking structure with a fire separation distance of 10 feet or greater shall not be limited.
406.3.7 Fire separation distance. Exterior walls and openings
in exterior walls shall comply with Tables 601 and 602.
The distance to an adjacent lot line shall be determined in
accordance with Table 602 and Section 705.
TABLE 602 d. Open parking garages complying with Section 406 shall not be required to have a fire-resistance rating.
Francis