Answers are for Illinois using the 1997 Illinois Accessibility Code:
a) Is tactile warning on doors to hazardous areas required in your jurisdiction? Yes IAC 400.310(t)(2)
b) Do you require tactile warning on stair doors? Yes at top of stair, not door IAC 400.310(t)(3)
c) If you do require tactile warning, what material/process do you allow? see code text below
d) If you require tactile warning on doors to hazardous areas, which rooms do you consider hazardous? see code text below
400.310 t) Detectable Warnings
Detectable warnings shall be provided as follows:
1) Detectable Warnings on Walking Surfaces. Detectable warning features
on walking surfaces shall consist of exposed aggregate concrete, cushioned
surfaces made of rubber or plastic, raised strips, or grooves. Features shall
contrast with that of the surrounding surface. Raised strips or grooves shall
comply with Illustration B, Fig. 40.
2) Tactile Warnings on Doors to Hazardous Areas. Doors that lead to areas
that might prove dangerous to a person who is visually impaired (for
example, doors to loading platforms, boiler rooms, stages, etc.) shall be
made identifiable to the touch by a textured surface on the door handle, knob,
pull, or other operating hardware. This textured surface may be made by
knurling or roughening or by a material applied to the contact surface. Such
textured surfaces shall not be provided for emergency exit doors or any doors
other than those to hazardous areas. See definition of "Hazardous Area".
3) Detectable Warnings at Stairs. All stairs, except those in dwelling units,
in enclosed stair towers, or set to the side of the path of travel shall have a
detectable warning at the top of stair runs (see Illustration B, Fig. 41).
4) Detectable Warnings at Hazardous Vehicular Areas. If a walk crosses or
adjoins a vehicular way, and the walking surfaces are not separated by curbs,
railings, or other elements between the pedestrian areas and vehicular
areas, the boundary between the areas shall be defined by a
continuous, detectable warning texture, which is 36 in. (915 mm) wide,
complying with subsection (t)(1) of this Section. (ADAAG 4.29.5)
5) Detectable Warnings at Reflecting Pools. The edges of reflecting pools
shall be protected by railings, walls, curbs, or detectable warnings complying
with subsection (t)(1) of this Section. (ADAAG 4.29.6)
6) Standardization. Textured surfaces for detectable warnings shall be
standard within a building, facility, site, or complex of buildings.