Tamper-resistant receptacle use question

SCBO1

REGISTERED
Joined
Oct 28, 2009
Messages
4,652
Location
MID WEST
During a final inspection it was noted that tamper-resistant receptacles were being used recessed on the top of a fireplace mantle, 54" above the floor.

Contractor replied "Watz dah probloom!"

My response: The ground part of the plug does not have the guard flapper inside the outlet to prevent dust build-up inside the plug.

Would you allow the TR receptacle in this application?

Would you allow the TR receptacle with child proof plug inserts when the outlets are not being used?

Would you allow weatherproof type outlets with covers?

Would you say, "tear it out and install an approved recess outlet with proper covers?

pc1
 
Pcinspector1 said:
During a final inspection it was noted that tamper-resistant receptacles were being used recessed on the top of a fireplace mantle, 54" above the floor.
Who 'noted' that and what art did they cite? The install is compliant although poor design IMO.
 
I certainly agree with Chris, TR receptacles are not required in that location nor probably the best choice but there's nothing in the code saying they can't be used to there.
 
406.12 Tamper-Resistant Receptacles in Dwelling Units.

Outlets more than 5.5' off the ground, do not need to be TR

54" above the floor need TR outlets
 
These receptacles are below the 5.5 ft above the floor exception requiring them to be TR type only. Does not require a floor type receptacle set-up with dust covers. This was NOTED on the inspection report as a "check code" to verify the set-up was compliant.

pc1
 
Pcinspector1 said:
These receptacles are below the 5.5 ft above the floor exception requiring them to be TR type only. Does not require a floor type receptacle set-up with dust covers. This was NOTED on the inspection report as a "check code" to verify the set-up was compliant.pc1
Nowhere in the Electrical Code does it require, that type of outlet, in that location, to have a dust cover.
 
You cannot have a receptacle mounted like that if the area where a work space or counter--406.5(E) otherwise it is fine. Why do you think they make these

White_SCRW.jpg
Access-Photocellb-sm.jpg


In the second picture the candle is plugged into the receptacle. We use these all the time
 
Actually we use them alot for kitchen cabinet receptacles rather than window sill... They are TR---http://www.sillites.com/