I have problems with some sprinkler and alarm deficiencies. I have noted the problems in my service reports, that were sent to the customer.
1. Leaking backflow, & antifreeze system plumbed so each time we test the flow, we loose antifreeze solution. The installer keeps saying all backflow devices leak. They do not have provision for a forward flow test, and no room to add provions for a forward flow test. Designed & built under 13-2007. Inspected and passed inspection.
2. An alarm system that does not unlock an exit path. Upgraded with new panel under 72-2007 in 2008. Inspection by State FM. Report sent to State FM, April 2009. The system has not been inspected by a contractor since our inspection of Feb 2009.
3. A secure drug and alcohol treatment for women and children that has no provision for a forward flow test. This has not passed the final inspection yet. Designed and built under 13-2007
4. A motel with a Cummins to power a generator that powers an electric fire pump that makes lots of noise. I do not think the pump will run long enough to control a fire in hte motel. The engine and pump are in a separate building, w/o heats, the tampers are not monitered by the FACP in the motel. Corporate is trying to find someone cheap to work on the pump. (Meaning they are too cheap to repair the pump) But they did pay to have the Cummins fixed and the mother board in the pump panel replaced. Corporate did not make those decisions, the motel manager did.
I am not wanting to be a tattle tale, but these places need to be to code. I do not even care if we do the work, as just so it is done and done to NFPA code. I may drop these accounts, unless I get fired first. We stay busy enough with those who want a good job, to deal with those who want crap work.
I have no problem sending letters to the local FM and State FM, but I do not want to appear to be a tattle tale. I am stuck between a rock and a hard place. Do you FMs take reports seriously and act upon them or just roll your eyes and junk them? Am I wasting my time?
Sometimes I think my goal in life is to be an troublemaker like ICE and Brudgers.
1. Leaking backflow, & antifreeze system plumbed so each time we test the flow, we loose antifreeze solution. The installer keeps saying all backflow devices leak. They do not have provision for a forward flow test, and no room to add provions for a forward flow test. Designed & built under 13-2007. Inspected and passed inspection.
2. An alarm system that does not unlock an exit path. Upgraded with new panel under 72-2007 in 2008. Inspection by State FM. Report sent to State FM, April 2009. The system has not been inspected by a contractor since our inspection of Feb 2009.
3. A secure drug and alcohol treatment for women and children that has no provision for a forward flow test. This has not passed the final inspection yet. Designed and built under 13-2007
4. A motel with a Cummins to power a generator that powers an electric fire pump that makes lots of noise. I do not think the pump will run long enough to control a fire in hte motel. The engine and pump are in a separate building, w/o heats, the tampers are not monitered by the FACP in the motel. Corporate is trying to find someone cheap to work on the pump. (Meaning they are too cheap to repair the pump) But they did pay to have the Cummins fixed and the mother board in the pump panel replaced. Corporate did not make those decisions, the motel manager did.
I am not wanting to be a tattle tale, but these places need to be to code. I do not even care if we do the work, as just so it is done and done to NFPA code. I may drop these accounts, unless I get fired first. We stay busy enough with those who want a good job, to deal with those who want crap work.
I have no problem sending letters to the local FM and State FM, but I do not want to appear to be a tattle tale. I am stuck between a rock and a hard place. Do you FMs take reports seriously and act upon them or just roll your eyes and junk them? Am I wasting my time?