Francis Vineyard
Virginia does not require permit for tents that are 900 sf or less and the IFC maintains compliance where reference by the IBC.
Does the code regulate tents and membrane structures of any size as an additional story in where erected on a roof without sides accordance with 503 but not a fire area?
The commentary addresses these sections as tents at grade.
IBC:
3102.1 General.
The provisions of Sections 3102.1 through :Next('./icod_ibc_2012_31_par012.htm')'>3102.8 shall apply to air-supported, air-inflated, membrane-covered cable and membrane-covered frame structures, collectively known as membrane structures, erected for a period of 180 days or longer. Those erected for a shorter period of time shall comply with the International Fire Code. Membrane structures covering water storage facilities, water clarifiers, water treatment plants, sewage treatment plants, greenhouses and similar facilities not used for human occupancy are required to meet only the requirements of :Next('./icod_ibc_2012_31_par005.htm')'>Sections 3102.3.1 and :Next('./icod_ibc_2012_31_par011.htm')'>3102.7. Membrane structures erected on a building, balcony, deck or other structure for any period of time shall comply with this section.
3102.4 Allowable floor areas.
The area of a membrane structure shall not exceed the limitations set forth in Table 503, except as provided in :Next('./icod_ibc_2012_5_par020.htm')'>Section 506.
3102.5 Maximum height.
Membrane structures shall not exceed one story nor shall such structures exceed the height limitations in feet set forth in Table 503.
Exception: Noncombustible membrane structures serving as roofs only.
FIRE AREA. The aggregate floor area enclosed and bounded by fire walls, fire barriers, exterior walls or horizontal assemblies of a building. Areas of the building not provided with surrounding walls shall be included in the fire area if such areas are included within the horizontal projection of the roof or floor next above.
IFC:
3103.8.4 Membrane structures on buildings.
Membrane structures that are erected on buildings, balconies, decks or other structures shall be regulated as permanent membrane structures in accordance with Section 3102 of the International Building Code.
Thanks in advance for your help.
IBC:
3102.1 General.
IFC: