In the 2018 IRC we have this test for Hydronic system test:
M2101.10 Tests. Hydronic piping systems shall be tested
hydrostatically at a pressure of one and one-half times the
maximum system design pressure, but not less than 100
pounds per square inch (689 kPa). The duration of each test
shall be not less than 15 minutes.
But when the system is embedded we have this test:
M2103.4 Testing. Piping or tubing to be embedded shall be
tested by applying a hydrostatic pressure of not less than 100
psi (690 kPa). The pressure shall be maintained for 30 minutes,
during which the joints shall be visually inspected for leaks.
In the 2018 IMC we have this section which is the same as in the IRC
1208.1 General. Hydronic piping systems shall be tested
hydrostatically at one and one-half times the maximum system
design pressure, but not less than 100 psi (689 kPa). The
duration of each test shall be not less than 15 minutes.
The next section (1209) is for embedded systems, but does not
say anything about testing. Why a difference? Is no test required?
In the 2018 IRC we have this test for Hydronic system test:
M2101.10 Tests. Hydronic piping systems shall be tested
hydrostatically at a pressure of one and one-half times the
maximum system design pressure, but not less than 100
pounds per square inch (689 kPa). The duration of each test
shall be not less than 15 minutes.
But when the system is embedded we have this test:
M2103.4 Testing. Piping or tubing to be embedded shall be
tested by applying a hydrostatic pressure of not less than 100
psi (690 kPa). The pressure shall be maintained for 30 minutes,
during which the joints shall be visually inspected for leaks.
In the 2018 IMC we have this section which is the same as in the IRC
1208.1 General. Hydronic piping systems shall be tested
hydrostatically at one and one-half times the maximum system
design pressure, but not less than 100 psi (689 kPa). The
duration of each test shall be not less than 15 minutes.
The next section (1209) is for embedded systems, but does not
say anything about testing. Why a difference? Is no test required?