My concern is for the penetration firestop foam known as 3M Fire Barrier Rated Foam FIP 1-Step. The product was tested per ASTM E 814/UL 1479 to afford itself 13 UL listings. This product then must be installed as tested according to 714.4.1.2 and 715.5.1.2. This product is a two part liquid that expands to five times its volume when mixed. Acts like an intumescent by expanding to fill voids left by melting penetrants but is not classified as one.
Why do I not consider this material a foam plastic insulation which requires it to contain a thermal barrier(1/2inch gypsum) as stated by 2603.4? Is it not thermosetting?
When expanded it is less than 20 pcf (lb/ft^3) and acts as a thermal insulator.
I really want to know if such a penetrating firestop system, that was tested as required by 714.4.1.2 and 715.5.1.2, has to also meet the requirement of a foam plastic insulation 2603.4?
Why do I not consider this material a foam plastic insulation which requires it to contain a thermal barrier(1/2inch gypsum) as stated by 2603.4? Is it not thermosetting?
When expanded it is less than 20 pcf (lb/ft^3) and acts as a thermal insulator.
Foam Plastic Insulation definition:
A plastic that is intentionally expanded by the use of a foaming agent to produce a reduced-density plastic containing voids consisting of open or closed cells distributed throughout the the plastic for thermal insulating or acoustical purposes and that has a density of less than 20 pounds per cubic foot (pcf).
I really want to know if such a penetrating firestop system, that was tested as required by 714.4.1.2 and 715.5.1.2, has to also meet the requirement of a foam plastic insulation 2603.4?