The 2023 NEC: Ground-Fault Protection of Equipment in Healthcare Facilities

Section 517.17 of the 2023 National Electrical Code (NEC) outlines ground-fault protection of equipment (GFPE) requirements for healthcare facilities. These provisions are essential for protecting critical systems and ensuring the safety and reliability of electrical infrastructure in environments that serve life-critical functions. Building officials and inspectors must understand these updated requirements and enforce them rigorously to maintain compliance and safeguard patient care.

Applicability (517.17(A))

The GFPE requirements in 517.17 apply to buildings or portions of buildings containing healthcare facilities with Category 1 spaces or those utilizing electrical life-support equipment. They also apply to buildings providing essential utilities or services for such spaces. This broad applicability means that GFPE provisions extend to:
  • Hospitals, which generally contain multiple Category 1 spaces.
  • Outpatient surgical centers within mixed-use buildings.
  • Any healthcare facility classified as providing critical care.
By contrast, most general medical or dental practices in multiple-occupancy buildings are exempt unless they meet the criteria of Category 1 care. Additionally, if GFPE is not provided at the service level, no second level of protection is required. For tenant buildouts or renovations in existing buildings, the introduction of healthcare facilities may necessitate compliance with second-level GFPE requirements. In such cases, careful analysis of the existing service equipment is crucial to avoid unnecessary disruptions.

Ground-Fault Protection for Feeders (517.17(B))

Where GFPE is applied at the service level, an additional level of protection is required downstream for all feeder disconnecting means. Key requirements include:
  • Use of overcurrent devices, current transformers, or equivalent protective equipment to ensure feeders open during a ground fault.
  • The prohibition of GFPE on the load side of an essential electrical system transfer switch. This ensures that the alternate power source—often a generator—remains operational during a fault.
Unlike Sections 210.13, 215.10, and 230.95, which mandate GFPE based on disconnecting means ratings (1000 amperes or more), 517.17(B) requires additional levels of GFPE to ensure selectivity between feeders and service-level devices. This approach prevents faults from causing widespread outages in a healthcare facility, limiting the impact to a single feeder.

Selectivity Requirements (517.17(C))

Section 517.17(C) emphasizes the importance of fully selective ground-fault protection to ensure faults are isolated to the feeder level without tripping the service device. Selectivity is achieved through precise coordination of the time-current characteristics of protective devices. This includes:
  • Ensuring feeder devices operate without tripping service devices during ground faults downstream of the feeder.
  • Following manufacturer’s recommendations for device settings.
  • Considering tolerances and disconnect operating times to achieve full selectivity.
Proper coordination ensures that critical systems remain operational during a ground fault, which is vital for patient safety and continuity of care in healthcare facilities.

Testing Requirements (517.17(D))

When GFPE is installed, it must undergo performance testing to verify compliance with Section 517.17(C). Testing must be conducted by qualified personnel using equipment-specific instructions. A written record of the testing process and results must be maintained and made available to the authority having jurisdiction (AHJ).

Testing ensures that:
  • All levels of ground-fault protection function as intended.
  • Protective devices coordinate effectively to isolate faults.
  • Systems meet the design specifications and safety requirements of the 2023 NEC.
Practical Considerations and Enforcement

Enforcing GFPE provisions in Section 517.17 requires inspectors and building officials to:
  • Verify the application of GFPE at both service and feeder levels for facilities meeting the applicability criteria.
  • Confirm that GFPE devices are installed in compliance with selectivity and testing requirements.
  • Ensure that written testing records are available and complete.
Special attention should be given to renovations or new tenant buildouts in mixed-use buildings, as these may introduce healthcare facilities requiring second-level GFPE. Inspectors should also ensure compliance with transfer switch provisions to prevent unintended interruptions of alternate power sources.

Summary of Key Points:
  • Section 517.17 applies to healthcare facilities with Category 1 spaces or life-support equipment.
  • GFPE must be applied at both service and feeder levels to ensure system reliability and safety.
  • Selectivity between feeder and service devices prevents widespread outages.
  • Testing is mandatory for all installed GFPE systems, with records maintained for AHJ review.
The 2023 NEC’s enhancements to GFPE requirements reflect the critical role of reliable electrical systems in healthcare environments. By enforcing these provisions, building officials and inspectors can ensure patient safety and the uninterrupted operation of essential systems.
 