• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

The Meaning of 2023 NEC 300.13(B) Multiwire Branch Circuits

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,075
Location
Somewhere Too Hot & Humid
(B) Device Removal.
In multiwire branch circuits, the continuity of a grounded conductor shall not depend on device connections such as lampholders, receptacles, and so forth where the removal of such devices would interrupt the continuity.

So what does that mean?

Grounded conductors (neutrals) of multiwire branch circuits supplying receptacles, lampholders, or other devices are not permitted to depend on terminal connections for continuity between devices. For multiwire installations, a splice can be made with a jumper connected to the terminal or the neutral can be looped. This allows a receptacle or device to be replaced without interrupting the continuity of energized downstream line-to-neutral loads. Opening the neutral could cause unbalanced voltages, and a considerably higher voltage would be impressed on one part of a multiwire branch circuit, especially if the downstream line-to-neutral loads were appreciably unbalanced.

In other words, these devices must be pigtailed and for a receptacle for example, you can't use all 4 terminals of a receptacle and feed through it.
 